[Nut-upsuser] mge galaxy 6000 three-phase supported or not?

Miroslav Shaltev miroslav.shaltev at shaltev.org
Tue Sep 25 05:02:27 UTC 2007


thank you Bernd,

broken snmp-ups is a pity.

Is there a chance to read the values with another adapter (mge-shut or 
mge-utalk)?


cheers,
miroslav


On Monday 24 September 2007, you wrote:
> Hi,
>
> > i just wonder, if it is posible to read the values for all the three
> > phases of a mge galaxy 6000 ups?
> >From looking at the mgemib part of the snmp-ups it doesn't read the data
>
> of all 3 phases (yet). Though this should be fairly easy to add. If the
> mge snmp adapter supports queries using the ietf mib that is another way
> to get that data. though ietfmib.h in the current version (and svn) is
> broken. (Arjen can you add the patch i sent you a while ago? ietfmib.h
> uses the wrong OID for the query)
> And all snmp-ups driven upsen don't support shutdowns properly (yet).
> I'm currently looking at that part for powerware upsen (using ietfmib
> and pwmib).
>
> > can someone post the upsc from such ups?
>
> I could only provide that for powerware upsen:
>
> driver.version.internal: 0.42 (mib: ietf 1.3)
> input.L1-N.voltage: 231.0
> input.L1.current: 2.0
> input.L2-N.voltage: 231.0
> input.L2.current: 2.0
> input.L3-N.voltage: 232.0
> input.L3.current: 3.0
> input.phases: 3.0
>
>
> driver.version.internal: 0.42 (mib: pw 0.6)
> input.bypass.L1-N.voltage: 232.0
> input.bypass.L2-N.voltage: 0.0
> input.bypass.L3-N.voltage: 0.0
> input.frequency: 50.1
> input.L1-N.voltage: 232.0
> input.L1.current: 2.0
> input.L2-N.voltage: 232.0
> input.L2.current: 3.0
> input.L3-N.voltage: 233.0
> input.L3.current: 3.0
> input.phases: 3.0
>
>
>  Bernd



-- 
SHALTEV.ORG @ http://www.shaltev.org