[Nut-upsuser] [Bulk] Re: Configuring a server without an UPS attached

Steve T stevetucknott at yahoo.co.uk
Fri Aug 22 12:37:47 UTC 2008


Charles,
Thanks for that. 
I think the duplicated startup was caused by me also
editing /etc/sysconfig/ups as well as the NUT specific config files. I
have removed the /etc/sysconfig changes and the messages file looks ok
(comparatively!).


On Fri, 2008-08-22 at 08:20 -0400, Charles Lepple wrote:
> On Aug 22, 2008, at 7:18 AM, Steve T wrote:
> 
> 
> 
> > This will sound a bit odd.
> > I have a current server running with a UPS. I'm in the process of
> > replacing that server with another and obviously want Nut to monitor
> > the new server. The new/old servers are in different locations, so I
> > don't have access to the UPS while configuring the replacement
> > server.
> > I think I have the config ok, but what errors would you expect to
> > see? Typically I'm getting a 'driver not connected' type error in
> > the /var/log/messages:
> > 
> 
> 
> "driver not connected" is normal. However...
> 
> 
> 
> > Aug 19 18:07:16 T300 upsd[1308]: listening on 0.0.0.0 port 3493
> > Aug 19 18:07:16 T300 upsd[1308]: Can't connect to UPS [belkin]
> > (belkinunv-belkin): No such file or directory
> > Aug 19 18:07:16 T300 upsd[1309]: Startup successful
> > Aug 19 18:07:16 T300 upsmon[1312]: Startup successful
> > Aug 19 18:07:16 T300 upsd[1309]: Client nutmon at 127.0.0.1 logged into
> > UPS [belkin]
> > Aug 19 18:07:16 T300 upsmon[1313]: Poll UPS [belkin at localhost]
> > failed - Driver not connected
> > Aug 19 18:07:16 T300 upsmon[1313]: Communications with UPS
> > belkin at localhost lost
> > Aug 19 18:07:21 T300 upsmon[1313]: Poll UPS [belkin at localhost]
> > failed - Driver not connected
> > Aug 19 18:07:21 T300 upsmon[1313]: UPS belkin at localhost is
> > unavailable
> > Aug 19 18:07:26 T300 upsmon[1313]: Poll UPS [belkin at localhost]
> > failed - Driver not connected
> > Aug 19 18:07:29 T300 upsd[1342]: not listening on 0.0.0.0 port 3493
> > Aug 19 18:07:29 T300 upsmon[1347]: Startup successful
> > Aug 19 18:07:29 T300 upsd[1309]: Client nutmon at 127.0.0.1 logged into
> > UPS [belkin]
> > Aug 19 18:07:29 T300 upsmon[1348]: Poll UPS [belkin at localhost]
> > failed - Driver not connected
> > Aug 19 18:07:29 T300 upsmon[1348]: Communications with UPS
> > belkin at localhost lost
> > Aug 19 18:07:31 T300 upsmon[1313]: Poll UPS [belkin at localhost]
> > failed - Driver not connected
> > Aug 19 18:07:34 T300 upsmon[1348]: Poll UPS [belkin at localhost]
> > failed - Driver not connected
> > Aug 19 18:07:34 T300 upsmon[1348]: UPS belkin at localhost is
> > unavailable
> > Aug 19 18:07:36 T300 upsmon[1313]: Poll UPS [belkin at localhost]
> > failed - Driver not connected
> > Aug 19 18:07:39 T300 upsmon[1348]: Poll UPS [belkin at localhost]
> > failed - Driver not connected
> > Aug 19 18:07:41 T300 upsmon[1313]: Poll UPS [belkin at localhost]
> > failed - Driver not connected
> 
> 
> Having two copies of upsmon (1313 and 1348) logging messages about the
> same UPS is not expected, though.
> 
> 
> Also note:
> 
> 
> > Aug 19 18:07:16 T300 upsd[1308]: listening on 0.0.0.0 port 3493
> 
> [...]
> > Aug 19 18:07:29 T300 upsd[1342]: not listening on 0.0.0.0 port 3493
> 
> 
> 
> The second copy of upsd can't bind to the same port as the first one,
> so you get the above error message.
> 
> 
> 
> -- 
> Charles Lepple
> clepple at gmail
> 
> 
> 
> 
> 
> 
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20080822/3c6f71f9/attachment.htm 


More information about the Nut-upsuser mailing list