[Nut-upsuser] MGE pulsar evolution 3000 discharges without nut noticing
Aaron J. Grier
agrier at poofygoof.com
Wed Feb 20 04:55:08 UTC 2008
I'm running nut 2.0.1 with an MGE pulsar evolution 3000 with the
mge-utalk (serial) driver on NetBSD 3.1 .
I had a very strange occurance in my basement datacenter this early AM.
the following was logged by upslog:
20080219 023452 100.0 123.0 049.0 [OL CHRG] NA 60.00
20080219 023522 100.0 122.8 049.0 [OL CHRG] NA 60.00
20080219 023552 098.0 123.0 049.0 [OL DISCHRG] NA 60.00
20080219 023622 097.0 123.0 049.0 [OL DISCHRG] NA 60.00
...
20080219 063429 019.0 122.6 049.0 [OL DISCHRG] NA 60.00
20080219 063459 019.0 122.8 049.0 [OL DISCHRG] NA 60.00
20080219 183013 100.0 121.1 050.0 [OL CHRG] NA 60.00
20080219 183043 100.0 120.9 049.0 [OL CHRG] NA 60.00
the good news is the UPS held up for four hours.
the bad news is that nut completely ignored that the UPS was
discharging, and none of my connected machines shut down properly. I
know that the UPS driver was running, because if was not, upsd would
have complained loudly and frequently. I know upsd was running (on the
connected server as well as all the clients), because if it was not,
upsmon would have complained loudly and frequently.
there were no indications in my logs that nut was paying any attention
to the situation.
why did my UPS decide to discharge its battery when there appears to be
no power outage? (just looking for suggestions and guesses here from
other MGE users...)
why did nut not see that my UPS was discharging and the battery
percentage running down and take appropriate action? "OL DISCHRG"
status in the logs seems nonsensical. I have only seen this condition a
few times before in my logs:
20061002 002628 094.0 079.6 045.0 [OB DISCHRG] NA 60.00
20061002 002658 093.0 096.8 045.0 [OL DISCHRG BOOST] NA 60.00
20061002 002728 093.0 088.3 045.0 [OL DISCHRG] NA 60.00
20061002 002758 093.0 000.0 045.0 [OB DISCHRG] NA 00.00
Oct 2 00:22:59 aragorn upsmon[234]: UPS mge3000 at localhost on battery
Oct 2 00:26:45 aragorn upsmon[234]: UPS mge3000 at localhost on line power
Oct 2 00:27:35 aragorn upsmon[234]: UPS mge3000 at localhost on battery
nut saw this one, and shut everything down, as expected.
20061214 224604 100.0 122.4 054.0 [OL CHRG] NA 60.00
20061214 224634 099.0 123.7 056.0 [OL DISCHRG] NA 60.00
20061214 224704 097.0 000.0 054.0 [OB DISCHRG] NA 00.00
Dec 14 22:46:45 aragorn upsmon[234]: UPS mge3000 at localhost on battery
Dec 14 22:58:41 aragorn upsmon[234]: UPS mge3000 at localhost battery is low
Dec 14 22:58:41 aragorn upsd[226]: Client master at 127.0.0.1 set FSD on UPS [mge3000]
Dec 14 22:58:57 aragorn upsmon[234]: Host sync timer expired, forcing shutdown
Dec 14 22:58:57 aragorn upsmon[234]: Executing automatic power-fail shutdown
Dec 14 22:58:57 aragorn upsmon[234]: Auto logout and shutdown proceeding
Dec 14 22:59:02 aragorn upsd[226]: Host 127.0.0.1 disconnected (read failure)
Dec 14 22:59:08 aragorn upsd[226]: Signal 15: exiting
nut did not see this one, but it was transient:
20070227 083935 100.0 122.2 048.0 [OL CHRG] NA 60.00
20070227 084005 100.0 122.2 048.0 [OL DISCHRG] NA 60.00
20070227 084035 100.0 122.2 048.0 [OL CHRG] NA 60.00
here is the device (online now)
$ upsc mge3000 at localhost
battery.charge: 100.0
battery.charge.low: 30
battery.runtime: 00876
battery.voltage: 081.6
battery.voltage.nominal: 072.0
driver.name: mge-utalk
driver.parameter.port: /dev/tty00
driver.version: 2.0.1
driver.version.internal: 0.81.0
input.frequency: 60.00
input.transfer.boost.low: 102.0
input.transfer.high: 132.0
input.transfer.low: 102.0
input.transfer.trim.high: 132.0
input.voltage: 122.8
output.current: 010.3
output.voltage: 122.2
ups.delay.shutdown: 020
ups.delay.start: 001
ups.firmware: unknown
ups.id: Evolutio 3000 17
ups.load: 049.0
ups.mfr: MGE UPS SYSTEMS
ups.model: Evolution 3000
ups.status: OL CHRG
ups.test.interval: 10080
thanks in advance for any advice.
--
Aaron J. Grier | "Not your ordinary poofy goof." | agrier at poofygoof.com
More information about the Nut-upsuser
mailing list