[Nut-upsuser] Old APC SmartUPS 1250, Nut 2.2.2 Fedora 9

Don Harvie donharvie at yahoo.com.au
Mon Jul 14 04:57:15 UTC 2008


Charles Lepple wrote:
>> Don,
>>
>> just for completeness, what does 'upsc' return for the old 1250 with
>> the patched driver?
>>
>> (You may remove the serial number if you prefer - I'm just checking to
>> be sure we're getting sane values for everything.)

Hi Charles,

upsc output below with the patched driver:
(Yes the batteries are stuffed - waiting for pay day ;-)

Thx,
Don H

$ upsc smartups1250 at localhost
battery.alarm.threshold: N
battery.charge: 100.0
battery.charge.restart: 90
battery.date: 11/20/04
battery.runtime: 6480
battery.runtime.low: 120
battery.voltage: 27.54
battery.voltage.nominal: 024
driver.name: apcsmart
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ttyS0
driver.version: 2.2.2
driver.version.internal: 1.99.8
input.frequency: 50.00
input.quality: FF
input.sensitivity: L
input.transfer.high: 264
input.transfer.low: 204
input.transfer.reason: O
input.voltage: 243.0
input.voltage.maximum: 246.7
input.voltage.minimum: 243.0
output.voltage: 243.0
output.voltage.nominal: 220
ups.delay.shutdown: 300
ups.delay.start: 300
ups.id: adler
ups.load: 000.0
ups.mfr: APC
ups.mfr.date: 08/24/95
ups.model: Smart-UPS
ups.serial: 07025563
ups.status: OL
ups.temperature: 018.4
ups.test.interval: 0
ups.test.result: NO
 



More information about the Nut-upsuser mailing list