> If you have any more questions regarding this, please use the nut-upsuser
> mailinglist instead.
Redirected to the appropriate list, sorry.
> > Is there a place in the upsmon.conf (or elsewhere)
> > file where one may enter something like:
> >
> > OVERRIDE_BATTERY_CHARGE_LOW 20
> > OVERRIDE_BATTERY.LOW 240
> >
> See 'man 8 upsrw'. If your UPS supports changing this value, it should be
> listed if you run 'upsrw <upsname>'. Most of the time, if it is possible
> to change this value, it will be stored in non-volatile memory in the UPS
> itself, so you only need to do this once.
upsrw listed the values that may be changed, but it would not change
them. When I try it asks for a username/password. I tried root,
nut (the user "built into" nut), and the single user entry in
upsd.users. In all cases this happened:
% /usr/local/ups/bin/upsrw -s battery.charge.low=25 -u root
apcups at localhost
Password:
Unexpected response from upsd: ERR ACCESS-DENIED
This is nut 2.2.2 built from source.
Possibly relevant, the password for the upsd.users account is 23
characters long. Too long for the software maybe??? It works ok
with upsmon though.
Thanks,
David Mathog
mathog at caltech.edu
Manager, Sequence Analysis Facility, Biology Division, Caltech