Hi,
Apologies for picking up on this old thread but I never had gotten this
issue resolved and I'm now back in the location where the UPSs are so I was
hoping we could look into the issue again.

Basically, I had two Unitek Alpha 1200sx UPSs, connected to Fedora Linux 8.
The NUT version seems to be:

Network UPS Tools upsd 2.2.0-
not listening on 0.0.0.0 port 3493

The driver seems to be the megatec_usb driver. The problem I have is that
this only seems to work occasionally (I typically have to restart the deamon
several times, switch on/off the UPSs etc in order to get it to work). Most
of the time, the controller seems to fail to start up and I subsequently get
the following message:

Broadcast message from nut (Tue Oct  7 21:14:44 2008):

UPS unial1200 at localhost is unavailable

I'm not quite sure what other information you'd need. That said, I can
provide any output requested.

Thanks in advance for helping me out.

Joe


On Sat, Jan 5, 2008 at 12:15 PM, Joseph Borg <juu.borg at gmail.com> wrote:

> Hi,
> The sub-driver is agiler. The requested output follows:
>
> ---------------
> Network UPS Tools 2.2.0- - Megatec protocol driver 1.5.4 [megatec_usb]
> Carlos Rodrigues (c) 2003-2007
>
> Serial-over-USB transport layer for Megatec protocol driver [megatec_usb]
>
> debug level is '5'
> Checking device (0000/0000) (002/001)
> - VendorID: 0000
> - ProductID: 0000
> - Manufacturer: unknown
> - Product: unknown
> - Serial Number: unknown
> - Bus: 002
> Trying to match device
> Device does not match - skipping
> Checking device (0000/0000) (001/001)
> - VendorID: 0000
> - ProductID: 0000
> - Manufacturer: unknown
> - Product: unknown
> - Serial Number: unknown
> - Bus: 001
> Trying to match device
> Device does not match - skipping
> Checking device (0F03/0001) (001/002)
> - VendorID: 0f03
> - ProductID: 0001
> - Manufacturer: Ver 1.0
> - Product: USB To RS232 Interface (V1.0) BaudRate 2400bps
> - Serial Number: unknown
> - Bus: 001
> Trying to match device
> Device matches
> failed to claim USB device, trying 2 more time(s)...
> detaching kernel driver from USB device...
> trying again to claim USB device...
>
> Broadcast message from nut (Sat Jan  5 12:10:56 2008):
>
> Communications with UPS unial1200 at localhost lost
> Starting UPS detection process...
> Attempting to detect the UPS...
> Sending "Q1" command...
> "Q1" command successful.
> Attempting to detect the UPS...
> Sending "Q1" command...
> "Q1" command successful.
> Attempting to detect the UPS...
> Sending "Q1" command...
> "Q1" command successful.
> Attempting to detect the UPS...
> Sending "Q1" command...
> "Q1" command successful.
> Attempting to detect the UPS...
> Sending "Q1" command...
> "Q1" command successful.
> 0 out of 5 detection attempts failed (minimum failures: 2).
> Asking for UPS information ("I" command)...
> UPS information: #UNITEK          Alph1200Sx A1
> Megatec protocol UPS detected [UNITEK Alph1200Sx A1].
> Asking for UPS power ratings ("F" command)...
> UPS power ratings: #230.0 4.3 24.00 50.0
> Asking for UPS status ("Q1" command)...
> UPS status: (230.0 230.0 2>3.0 016 50.0 29.0 32.0 00001000
> 24.0V battery, present voltage (0.0V) outside of supported intervals.
> This UPS has an unsupported combination of battery voltage/number of
> batteries.
> Cannot calculate charge percentage for this UPS.
> Done setting up the UPS.
> Asking for UPS status ("Q1" command)...
> UPS status: ( 230.0 230.0 353.0 016 50.0 28.8 32.0 00001000
> dstate_init: sock /var/run/nut/megatec_usb-unial1200 open on fd 5
> Asking for UPS status ("Q1" command)...
> UPS status: (230.0 230.0 2>3.0 016 50.0 28.8 32.0 00001000
> Asking for UPS status ("Q1" command)...
> UPS status: (230.0 230.0 323.4 016 50.0 29.0 32.0 00001000
> Asking for UPS status ("Q1" command)...
> UPS status: (230.0 230.0 302.> 016 50.0 28.8 32.0 00001000
> Asking for UPS status ("Q1" command)...
> --------------------
> As noted in the previous email, the driver doesn't always load sucessfully
> and I have to switch off the UPs to sort this out. I'm now sure if this is a
> known/limitation/driver incompatibility/some tweak I have to do. That said,
> when the driver does load, then everything seems fine.
>
> I also suspect that all the other Unitek Alpha YYYYsx models should work
> since they seem to me to be the same as my 1200sx one; only a different VA.
>
> Cheers,
>
> Joe
>
>
>
>
>
> On Jan 4, 2008 7:46 PM, Alexander I. Gordeev <lasaine at lvk.cs.msu.su>
> wrote:
>
>> On Thu, 03 Jan 2008 21:33:32 +0300, Joseph Borg <juu.borg at gmail.com>
>> wrote:
>>
>> > Just a small update; I figured out the udev script so now the processes
>> > don't run as root and all still works :-). Thanks for all your help. The
>> > only remaining issue is the intermittant failures when the driver is
>> > loading..
>> >
>> > Joe
>> >
>>
>> Could you please provide the output of the actual driver, like this:
>>
>> megatec_usb -a myups -DDDDD
>>
>> Do you use agiler subdriver? Then I'll add your UPS to the list of
>> supported devices.
>>
>> --
>>   Alexander
>>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20081007/0b10931d/attachment.htm 


More information about the Nut-upsuser mailing list