[Nut-upsuser] APC UPS won't restart after power outage

Ole Hoppe ole.hoppe at gmail.com
Tue Dec 22 19:13:51 UTC 2009


Hi

Installed new APC Back-UPS CS 350 on single server running openSUSE 11.2
64-bit and configured NUT 2.4.1 (SUSE package) according to instructions.

When testing, NUT shuts down the server correctly and instructs the UPS to
power down. UPS does so after some 20s delay, everything without errors. But
after restoring main power, even after waiting for 1/2h UPS does not by
itself turn on again, all LEDs are dark. One has to manually press the UPS's
power button, which makes server and monitor run again immediately.

What could be wrong that prevents UPS from turning itself on again?

Below output of upsc:

battery.charge: 95
battery.charge.low: 10
battery.charge.warning: 50
battery.date: 2009/10/11
battery.mfr.date: 2009/10/11
battery.runtime: 1237
battery.runtime.low: 180
battery.temperature: 29.2
battery.type: PbAc
battery.voltage: 13.6
battery.voltage.nominal: 12.0
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.1
driver.version.data: APC HID 0.93
driver.version.internal: 0.34
input.voltage: 122.0
input.voltage.nominal: 120
output.voltage: 115.0
output.voltage.nominal: 120.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.firmware: 805.q8.D
ups.firmware.aux: q8
ups.load: 49.0
ups.mfr: American Power Conversion
ups.mfr.date: 2009/10/11
ups.model: Back-UPS CS 350
ups.productid: 0002
ups.serial: 4B0941P71480
ups.status: OL CHRG
ups.test.result: No test initiated
ups.timer.reboot: 0
ups.timer.shutdown: -1
ups.vendorid: 051d

Thanks a lot for any hint!
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20091222/8b934c58/attachment.htm>


More information about the Nut-upsuser mailing list