[Nut-upsuser] Megatec driver floods logs #2 & mail notifications
Yury V. Zaytsev
yury at shurup.com
Mon Dec 28 20:28:10 UTC 2009
Hi!
On Mon, 2009-12-28 at 20:54 +0100, Arjen de Korte wrote:
> I don't understand what you mean with first and second goal. Please
> make a timeline with events and what you want to happen at each point
> in time.
OK, I will try to put it the other way around :-) (let's assume that the
UPS battery is fully charged for clarity)
1) If the power goes down but then comes back within 1-3 minutes do
nothing (don't send emails etc.)
2) If the power goes down for longer then 3 minutes send a power down
e-mail.
3) If the power comes back send a power back e-mail and cancel shutdown.
4) If the power does not come back and the battery is drained (in my
tests in can last for ~15 minutes) shutdown the machine and hope for the
best.
So far I was not able to achieve this by simple means. So I settled with
the following setup:
# The timers, here 3 min after the ONBATT (ups on battery) event
AT ONBATT * START-TIMER linedown 180
# Cancel the countdown is power is back
AT ONLINE * CANCEL-TIMER linedown
AT ONLINE * EXECUTE lineup
It sends a power back e-mail no matter what, but probably we can live
with it.
Thanks!
--
Sincerely yours,
Yury V. Zaytsev