[Nut-upsuser] ordered shutdown
    Arjen de Korte 
    nut+users at de-korte.org
       
    Mon Feb  9 10:33:46 UTC 2009
    
    
  
Citeren Lars Täuber <taeuber op bbaw.de>:
> it seems I understood how NUT works now. But then it is not the  
> solution for us. The reason simply is we have one big ups for so  
> many servers. And it's a bad idea to have one point in time to  
> shutdown all servers. So one »battery low« signal for all servers is  
> not what we need.
In that case, I probably don't understand what you're trying to do.
> There are some servers that should  work as long as possible and  
> shut down shortly (2 minutes) before the ups shuts off. But these  
> server also should try to shut down and that's why they need the  
> connection to the ups too.
So you want the servers to keep running as long as possible and the  
clients should go down after a power outage of (say) five minutes?  
That's possible too.
> Is it possible with NUT to tell upsd to initiate a shutdown by the  
> means of upssched? As long as I understood upssched doesn't run as  
> root. So it can't be used to initiate a shutdown directly.
Sure. But if you can describe more clearly what you're trying to do,  
we might come up with other alternatives as well, as I don't think  
this is what you want to do.
Best regards, Arjen
-- 
Please keep list traffic on the list
    
    
More information about the Nut-upsuser
mailing list