[Nut-upsuser] Tripplite Smart1500
    Arjen de Korte 
    nut+users at de-korte.org
       
    Sun Jun  7 16:51:11 UTC 2009
    
    
  
Citeren Charles Lepple <clepple op gmail.com>:
>> ups.status:
>
> The "ups.status" value is problematic - it should include at least OL
> or OB. Not sure whether it is due to Protocol 4-related changes, or
> the aforementioned timeout.
The above is due to a problem with calculation of the size of reports  
in libhid.c that was fixed more than a year ago. This fix requires  
nut-2.2.2 or newer. For many USB devices, anything earlier than that  
may mean that they run into this limitation (that existed since we  
first released newhidups by the way).
Best regards, Arjen
-- 
Please keep list traffic on the list
    
    
More information about the Nut-upsuser