[Nut-upsuser] upsmon says ONBATT when status: TRIM
Lionel Elie Mamane
lionel at mamane.lu
Sat Jun 20 08:34:09 UTC 2009
On Sat, Jun 20, 2009 at 09:23:19AM +0200, Kjell Claesson wrote:
>> I've been getting emails from upsmon saying:
>> Subject: UPS PW5125 at localhost notification: ONBATT
>> UPS PW5125 at localhost on battery
>> But then the machines on the UPS stay on for hours; we haven't got
>> that kind of runtime, more like 10-20 minutes.
>> After a few occurrences, it now happened at a time where I could log
>> in to see in real time what is happening and:
>> $ upsc PW5125 | grep status
>> ups.status: TRIM
> This is fixed in a later release of the driver.
> And also if you upgrade to a later release you have load segment control
> and some more info from the PW5125 you run.
> Like this:
> ~ $ upsc pw5115
> input.frequency.high: 54
> input.frequency.low: 46
> input.transfer.boost.high: 207
> input.transfer.high: 266
> input.transfer.low: 171
> input.transfer.trim.low: 243
> outlet.1.*
> outlet.2.*
Great! Thanks for the info, and for the commit. I'll schedule an
upgrade for when downtime would be acceptable. (As it will be an
upgrade from 2.2 to 2.4, I prefer to take the opportunity to test the
automatic shutdown procedure again, especially with the Windows
clients and all that. And being extra cautious and all that.)
--
Lionel