[Nut-upsuser] APC Smart UPS 900i
Arjen de Korte
nut+users at de-korte.org
Thu May 28 07:35:05 UTC 2009
Citeren Rene Bartsch <ML op Bartschnet.de>:
> Command: "upsc su900i"
>
> ------------------------------------------ snip
> -----------------------------------------------
>
> battery.alarm.threshold: 0
> battery.charge: 100.0
> battery.charge.restart: 10
> battery.date: 11/02/01
> battery.runtime: 4440
> battery.runtime.low: 120
> battery.voltage: 27.67
> battery.voltage.nominal: 024
> driver.name: apcsmart
> driver.parameter.cable: 940-0024C
> driver.parameter.pollinterval: 2
> driver.parameter.port: /dev/ttyUSB0
> driver.version: 2.4.1
> driver.version.internal: 2.03
> input.frequency: 50.00
> input.quality: FF
> input.sensitivity: H
> input.transfer.high: 253
> input.transfer.low: 196
> input.transfer.reason: O
> input.voltage: 229.4
> input.voltage.maximum: 231.8
> input.voltage.minimum: 229.4
> output.voltage: 229.4
> output.voltage.nominal: 225
> ups.delay.shutdown: 180
> ups.delay.start: 300
> ups.id: UPS_IDEN
> ups.load: 006.2
> ups.mfr: APC
> ups.mfr.date: 02/18/93
> ups.serial: 00016325
> ups.status: OL
> ups.temperature: 045.9
> ups.test.interval: 0
> ups.test.result: NO
>
>
> ------------------------------------------ snap
> -----------------------------------------------
>
>
> Many thanks for the fast help! :)
Glad we could help you out here. I only see that I accidentally also
removed the ups.model, so I'll fix that later today. This should be
fairly easy to add back.
Best regards, Arjen
--
Please keep list traffic on the list
More information about the Nut-upsuser
mailing list