I finally resolve my problem, I just make symbolic link:
[test at box var/run/]# ln -s -T /var/state/ups/ nut
Now I finally got services online:
# /sbin/service ups start
Starting UPS driver controller: [ OK ]
Starting upsd: [ OK ]
Starting UPS monitor (master): [ OK ]
BUT, on upsc I got:
# upsc mustek
battery.charge: 100.0
battery.voltage: 27.50
battery.voltage.nominal: 24.0
driver.name: megatec_usb
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.2.0-
driver.version.internal: 1.5.4
input.frequency: 50.0
input.voltage: 201.7
input.voltage.fault: 201.2
input.voltage.maximum: 202.2
input.voltage.minimum: 199.8
output.voltage: 200.1
output.voltage.nominal: 220.0
ups.beeper.status: disabled
ups.delay.shutdown: 0
ups.delay.start: 2
ups.load: 26.0
ups.mfr: unknown
ups.model: unknown
ups.serial: unknown
ups.status: OL
ups.temperature: 25.0
I use megatec_usb driver and try with blazer_usb and same situation, I don`t
got ups.model/serial/mfr.
On shutdown (when battery is low), my ups shutdown strange, got off all led
and when I put power again, I must press power button to "turn off" ups and
press it again, to get the power.
What do you think what is the problem?!
Thank you.
-----Original Message-----
From: nut-upsuser-bounces+vladimir=micovic.com at lists.alioth.debian.org
[mailto:nut-upsuser-bounces+vladimir=micovic.com at lists.alioth.debian.org] On
Behalf Of Kjell Claesson
Sent: Wednesday, December 29, 2010 10:20 AM
To: nut-upsuser at lists.alioth.debian.org
Subject: Re: [Nut-upsuser] help with CyberPower 425HG
Hi James,
> $ sudo upsdrvctl start
> Network UPS Tools - UPS driver controller 2.4.3 Network UPS Tools -
> Generic HID driver 0.34 (2.4.3) USB communication driver 0.31 Using
> subdriver: CyberPower HID 0.3
>
OK, the driver seems to start.
But have you started the daemon (upsd)?
> $ sudo upsc myups at localhost
> Error: Driver not connected
Then you have to start the upsmon to monitor the ups.
---------
Check with:
ps xau |grep nut
nut 5324 0.0 0.0 12428 508 ? Ss 09:41 0:00
/lib/nut/bcmxcp -a pw5115
nut 5348 0.0 0.0 40528 864 ? Ss 09:41 0:00
/usr/sbin/upsd
nut 5367 0.0 0.0 40496 1148 ? S 09:41 0:00
/usr/sbin/upsmon
-------------
You may also do:
ps xau |grep ups