[Nut-upsuser] HP R1500 G2 UPS
Schupfer Stephan
Stephan.Schupfer at ksengineers.at
Fri Feb 19 09:42:30 UTC 2010
Hi Arnaud,
Here's the upsc output. I Can confirm that shutdown is working too at the moment - we have to do further testing. But currently I'm running on the unpatched 2.4.1 version with bcmxcp.
dacoks20dx:~# upsc HPR1500 at localhost
ambient.temperature: 53
ambient.temperature.high: 75
battery.charge: 89
battery.runtime: 1476
battery.voltage: 36.38
driver.name: bcmxcp
driver.parameter.baud_rate: 9600
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ttyS1
driver.version: 2.4.1
driver.version.internal: 0.21
input.frequency: 50.34
input.frequency.high: 55
input.frequency.low: 45
input.frequency.nominal: 50
input.transfer.boost.high: 207
input.transfer.high: 266
input.transfer.low: 194
input.transfer.trim.low: 243
input.voltage: 228
input.voltage.nominal: 230
outlet.1.delay.shutdown: -1
outlet.1.delay.start: 0
outlet.1.id: 1
outlet.1.status: On
outlet.2.delay.shutdown: -1
outlet.2.delay.start: 1
outlet.2.id: 2
outlet.2.status: On
output.current: 1.9
output.current.nominal: 6.4
output.frequency: 50.34
output.phases: 1
output.voltage: 228
output.voltage.nominal: 230
ups.alarm: BATTERIES_DISCONNECTED
ups.beeper.status: muted
ups.firmware: Cont:02.00 Inve:02.00
ups.load: 29.3
ups.model: HP R1500 G2 1500VA
ups.power: 439
ups.power.nominal: 1500
ups.serial: 3C88431991
ups.status: ALARM OL
-----Ursprüngliche Nachricht-----
Von: Arnaud Quette [mailto:aquette.dev at gmail.com]
Gesendet: Donnerstag, 18. Februar 2010 18:39
An: Schupfer Stephan
Cc: nut-upsuser at lists.alioth.debian.org
Betreff: Re: [Nut-upsuser] HP R1500 G2 UPS
2010/2/18 Schupfer Stephan <Stephan.Schupfer at ksengineers.at>:
> Hi Arnaud,
>
> Thank you for that info - that was quite important to me to know to get it working - so now i have communication over serial port with bcmxcp.
can you please confirm that at least shutdown is working.
sending back an upsc output would also be nice.
while waiting for the USB side completion, I'll add the serial
compatibility for 2.4.2 (due for tomorrow!).
cheers,
Arnaud
--
Linux / Unix Expert R&D - Eaton - http://www.eaton.com/mgeops
Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/
Debian Developer - http://www.debian.org
Free Software Developer - http://arnaud.quette.free.fr/
More information about the Nut-upsuser
mailing list