[Nut-upsuser] USB problems

Jason Englander jasoneng3 at gmail.com
Mon May 10 18:37:27 UTC 2010


On Mon, 10 May 2010, James wrote:

> Network UPS Tools - UPS driver controller 2.4.3
> Network UPS Tools - Generic HID driver 0.34 (2.4.3)
> USB communication driver 0.31
> Using subdriver: CyberPower HID 0.3
> libusb_get_report: could not claim interface 0: Device or resource busy
> Got disconnected by another driver: Device or resource busy
> Can't initialize data from HID UPS
> Driver failed to start (exit status=1)

FYI, I got that error yesterday with NUT 2.4.3, kernel 2.6.33.3, and a 
CyberPower CP1500AVRLCD using usbhid-ups and it seems fine after applying 
this patch:

http://boxster.ghz.cc/projects/nut/changeset/2407?format=diff&new=2407

Bus 005 Device 002: ID 0764:0501 Cyber Power System, Inc. CP1500 AVR UPS
Device Descriptor:
   bLength                18
   bDescriptorType         1
   bcdUSB               1.10
   bDeviceClass            0 (Defined at Interface level)
   bDeviceSubClass         0
   bDeviceProtocol         0
   bMaxPacketSize0         8
   idVendor           0x0764 Cyber Power System, Inc.
   idProduct          0x0501 CP1500 AVR UPS
   bcdDevice            0.01
   iManufacturer           3 CPS
   iProduct                1  CP 1500C
   iSerial                 0
   bNumConfigurations      1
   Configuration Descriptor:
     bLength                 9
     bDescriptorType         2
     wTotalLength           34
     bNumInterfaces          1
     bConfigurationValue     1
     iConfiguration          0
     bmAttributes         0xc0
       Self Powered
     MaxPower               50mA
     Interface Descriptor:
       bLength                 9
       bDescriptorType         4
       bInterfaceNumber        0
       bAlternateSetting       0
       bNumEndpoints           1
       bInterfaceClass         3 Human Interface Device
       bInterfaceSubClass      0 No Subclass
       bInterfaceProtocol      0 None
       iInterface              0
         HID Device Descriptor:
           bLength                 9
           bDescriptorType        33
           bcdHID               1.10
           bCountryCode           33 US
           bNumDescriptors         1
           bDescriptorType        34 Report
           wDescriptorLength     387
          Report Descriptors:
            ** UNAVAILABLE **
       Endpoint Descriptor:
         bLength                 7
         bDescriptorType         5
         bEndpointAddress     0x81  EP 1 IN
         bmAttributes            3
           Transfer Type            Interrupt
           Synch Type               None
           Usage Type               Data
         wMaxPacketSize     0x0008  1x 8 bytes
         bInterval              10
Device Status:     0x0001
   Self Powered


Also FYI, the hardware compatibility list lists cyberpower or powerpanel 
under the Cyber Power section, but the cyberpower driver appears to have 
been removed from the source at some point.  I had configure build 
usbhid-ups, powerpanel, and cyberpower in case I tried it via serial cable 
at some point in the future, cyberpower failed.

   Jason

-- 
Jason Englander <jason at englanders.us>
394F 7E02 C105 7268 777A  3F5A 0AC0 C618 0675 80CA




More information about the Nut-upsuser mailing list