[Nut-upsuser] Setting offdelay and ondelay in Smart-UPS 1500 RM units
Arjen de Korte
nut+users at de-korte.org
Thu Nov 11 18:57:39 UTC 2010
Citeren Javier Miqueleiz <javier op miqueleiz.com>:
> This unit uses a different HID path than the stardard one for sending a
> "load.on.delay" command. As the driver (usbhid-ups) can't find this command,
> it has to revert to rebooting the UPS. The HID paths involved are:
>
> - "UPS.PowerSummary.DelayBeforeStartup": the standard command for triggering
> a "load.on.delay" in USB units.
> - "UPS.Output.DelayBeforeStartup": used in this unit for triggering a
> "load.on.delay". The former doesn't exist.
Please run the following command
/path/to/usbhid-ups -DDD -a upsname > Smart-UPS1500RM.log 2>&1
Make sure to kill any usbhid-ups drivers lingering in the background
before running this command. Wait 15 seconds and then kill it with
Ctrl-C. Gzip the log file that is created and post it here.
> If you add the HID path "UPS.PowerSummary.DelayBeforeStartup" to "apc-hid.c",
> the driver will be able to use the "load.on.delay" command. And it
> will send a "load.on.delay", "load.off.delay" at shutdown.
We already have this mapping. Could it be that you actually meant
"UPS.Output.DelayBeforeStartup"? Posting the logs is sufficient, it
will provide us with all the information we need.
> With regards to "ondelay", the unit doesn't fully honor it. Seems to have its
> quirks on this.
We only support it if we can find the corresponding HID mapping.
> - offdelay>=0, ondelay=-1: the unit will shut down the load at the specified
> delay. And it will remain off. To turn it back on, the power-on button on the
> front panel must be pressed.
>
> - offdelay>=0, ondelay>offdelay: the unit will shut down the load at the
> specified delay. The UPS will turn it back on as soon as the external power
> is on. The "ondelay" is not honored in this case.
This is how it is supposed to work. The ondelay timer is only used in
case the power is present, otherwise the unit will switch on as soon
as the power returns. See also 'man 8 usbhid-ups' and the USB HID PDC
specifications. The only thing the driver can do is to set the timers.
It is up to the UPS how it deals with them (we can't control the UPS
when the power is out).
Best regards, Arjen
--