Citeren Kevin <bakdong op gmail.com>:
> You are quite right! I now have this line in apc-hid.c:
>
> { "shutdown.return", 0, 0,
> "UPS.APCGeneralCollection.APCDelayBeforeReboot", NULL, "1",
> HU_TYPE_CMD, NULL },
>
> and get this result:
>
> # clients/upscmd -u apcmon -p pass123 apc1500 shutdown.return
> Unexpected response from upsd: ERR CMD-NOT-SUPPORTED
>
> I have attached the output of "usbhid-ups -a apc1500 -k -DDD >
> CS500shutdown.txt 2>&1" in case it is of value.
It is of value. The HID path I sent was wrong (it isn't in the above
listing, so usbhid-ups will not find it). There is no
"APCGeneralCollection" in your UPS. Instead of
{ "shutdown.return", 0, 0,
"UPS.APCGeneralCollection.APCDelayBeforeReboot", NULL, "1",
HU_TYPE_CMD, NULL },
the correct HID path should be
{ "shutdown.return", 0, 0, "UPS.Output.APCDelayBeforeReboot",
NULL, "1", HU_TYPE_CMD, NULL },
Sorry about that.
Best regards, Arjen
--