[Nut-upsuser] Cyberpower CP850PFCLCD 120% battery charge

Justin Ellison justin at techadvise.com
Thu Mar 31 01:53:15 UTC 2011


Hello all,

I have a CyberPower Systems CP850PFCLCD that I'm hooking up to NUT 2.4.3
from apt running under Ubuntu 10.04.  Using the usbhid-ups driver, things
*seem* to work at first glance, but there are some odd issues.  The most
notable issue is that the battery.charge indicator reads 120 when at full
charge.  I came across this post here:
http://lists.alioth.debian.org/pipermail/nut-upsuser/2007-September/003222.htmlbut
it looks like the user never supplied the necessary data.

The other issue that I found was that the LB flag is sent way to early when
I unplugged the UPS from the outlet.  I captured a log of upsc polling every
5 seconds and I'm attaching to this message.  I'm more than happy to supply
debug output, but I don't know if you want me to unplug the UPS from the
outlet during that debug or not.

Thanks in advance for any help,

Justin


------------
ue Mar 29 23:30:39 CDT 2011
battery.charge: 120
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 450
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 16.0
battery.voltage.nominal: 24
device.mfr: CP850PFCLCD
device.model: CRDA103.981
device.serial: CPS
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.34
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 117.0
input.voltage.nominal: 120
output.voltage: 117.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 56
ups.mfr: CP850PFCLCD
ups.model: CRDA103.981
ups.productid: 0501
ups.realpower.nominal: 510
ups.serial: CPS
ups.status: OL
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764

Tue Mar 29 23:30:44 CDT 2011
battery.charge: 105
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 367
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 16.0
battery.voltage.nominal: 24
device.mfr: CP850PFCLCD
device.model: CRDA103.981
device.serial: CPS
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.34
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 0.0
input.voltage.nominal: 120
output.voltage: 120.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 56
ups.mfr: CP850PFCLCD
ups.model: CRDA103.981
ups.productid: 0501
ups.realpower.nominal: 510
ups.serial: CPS
ups.status: OB DISCHRG
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764

Tue Mar 29 23:30:49 CDT 2011
battery.charge: 96
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 360
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 16.0
battery.voltage.nominal: 24
device.mfr: CP850PFCLCD
device.model: CRDA103.981
device.serial: CPS
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.34
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 0.0
input.voltage.nominal: 120
output.voltage: 120.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 56
ups.mfr: CP850PFCLCD
ups.model: CRDA103.981
ups.productid: 0501
ups.realpower.nominal: 510
ups.serial: CPS
ups.status: OB DISCHRG
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764

Tue Mar 29 23:30:54 CDT 2011
battery.charge: 96
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 360
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 16.0
battery.voltage.nominal: 24
device.mfr: CP850PFCLCD
device.model: CRDA103.981
device.serial: CPS
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.34
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 0.0
input.voltage.nominal: 120
output.voltage: 120.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 56
ups.mfr: CP850PFCLCD
ups.model: CRDA103.981
ups.productid: 0501
ups.realpower.nominal: 510
ups.serial: CPS
ups.status: OB DISCHRG
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764

Tue Mar 29 23:30:59 CDT 2011
battery.charge: 87
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 304
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 16.0
battery.voltage.nominal: 24
device.mfr: CP850PFCLCD
device.model: CRDA103.981
device.serial: CPS
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.34
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 0.0
input.voltage.nominal: 120
output.voltage: 120.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 56
ups.mfr: CP850PFCLCD
ups.model: CRDA103.981
ups.productid: 0501
ups.realpower.nominal: 510
ups.serial: CPS
ups.status: OB DISCHRG
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764

Tue Mar 29 23:31:04 CDT 2011
battery.charge: 87
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 304
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 16.0
battery.voltage.nominal: 24
device.mfr: CP850PFCLCD
device.model: CRDA103.981
device.serial: CPS
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.34
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 0.0
input.voltage.nominal: 120
output.voltage: 120.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 56
ups.mfr: CP850PFCLCD
ups.model: CRDA103.981
ups.productid: 0501
ups.realpower.nominal: 510
ups.serial: CPS
ups.status: OB DISCHRG
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764

Tue Mar 29 23:31:09 CDT 2011
battery.charge: 83
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 290
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 16.0
battery.voltage.nominal: 24
device.mfr: CP850PFCLCD
device.model: CRDA103.981
device.serial: CPS
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.34
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 0.0
input.voltage.nominal: 120
output.voltage: 120.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 56
ups.mfr: CP850PFCLCD
ups.model: CRDA103.981
ups.productid: 0501
ups.realpower.nominal: 510
ups.serial: CPS
ups.status: OB DISCHRG
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764

Tue Mar 29 23:31:14 CDT 2011
battery.charge: 81
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 283
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 16.0
battery.voltage.nominal: 24
device.mfr: CP850PFCLCD
device.model: CRDA103.981
device.serial: CPS
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.34
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 0.0
input.voltage.nominal: 120
output.voltage: 120.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 56
ups.mfr: CP850PFCLCD
ups.model: CRDA103.981
ups.productid: 0501
ups.realpower.nominal: 510
ups.serial: CPS
ups.status: OB DISCHRG LB
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764

Tue Mar 29 23:31:19 CDT 2011
battery.charge: 79
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 276
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 16.0
battery.voltage.nominal: 24
device.mfr: CP850PFCLCD
device.model: CRDA103.981
device.serial: CPS
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.34
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 0.0
input.voltage.nominal: 120
output.voltage: 120.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 56
ups.mfr: CP850PFCLCD
ups.model: CRDA103.981
ups.productid: 0501
ups.realpower.nominal: 510
ups.serial: CPS
ups.status: FSD OB DISCHRG LB
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764

Tue Mar 29 23:31:24 CDT 2011
battery.charge: 78
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 253
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 16.0
battery.voltage.nominal: 24
device.mfr: CP850PFCLCD
device.model: CRDA103.981
device.serial: CPS
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.34
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 0.0
input.voltage.nominal: 120
output.voltage: 120.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 56
ups.mfr: CP850PFCLCD
ups.model: CRDA103.981
ups.productid: 0501
ups.realpower.nominal: 510
ups.serial: CPS
ups.status: FSD OB DISCHRG LB
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764

Tue Mar 29 23:31:29 CDT 2011
battery.charge: 74
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 222
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 16.0
battery.voltage.nominal: 24
device.mfr: CP850PFCLCD
device.model: CRDA103.981
device.serial: CPS
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.34
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 0.0
input.voltage.nominal: 120
output.voltage: 120.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 56
ups.mfr: CP850PFCLCD
ups.model: CRDA103.981
ups.productid: 0501
ups.realpower.nominal: 510
ups.serial: CPS
ups.status: FSD OB DISCHRG LB
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764

Tue Mar 29 23:31:34 CDT 2011
battery.charge: 74
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 222
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 16.0
battery.voltage.nominal: 24
device.mfr: CP850PFCLCD
device.model: CRDA103.981
device.serial: CPS
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.34
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 0.0
input.voltage.nominal: 120
output.voltage: 120.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 56
ups.mfr: CP850PFCLCD
ups.model: CRDA103.981
ups.productid: 0501
ups.realpower.nominal: 510
ups.serial: CPS
ups.status: FSD OB DISCHRG LB
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20110330/3db8513e/attachment-0001.htm>


More information about the Nut-upsuser mailing list