[Nut-upsuser] Powercom issues in NUT (was: PowerCom BNT2000AT ups on nut 2.6.0 - second try)
Angela Williams
angierfw at gmail.com
Wed May 18 11:57:00 UTC 2011
Hi All and Keven in particular!
On Tuesday 17 May 2011 at 18:38 Keven L. Ates :-
> Hmmm...
> I patched the "BNT-other" driver. You may want to try using that as
> an alternative driver, since you can specify ALL the settings for your
> UPS.
>
> But to address your problem, we can look at the system and its
> settings. The BNT type defaults as follows:
>
> /* Type */ "BNT",
> /* Number of Bytes */ 16,
> /* Flow Control */ { "no_flow_control", no_flow_control },
> /* Validation Bytes */ { { 11U, 0x42U }, { 8U, 0U }, { 8U, 0U } },
> /* Power Kill Delay */ { { 1U, 30U }, 'y' },
> /* Frequency */ { 0.00020803, 0.0 },
> /* Load % */ { 1.4474, 0.0, 0.8594, 0.0 },
> /* Battery % */ { 5.0000, 0.3268, -825.00, 0.46511, 0 },
> /* Voltage */ { 1.9216, -0.0977, 0.82857, 0.0000 },
>
> You have:
>
> driver = powercom
> type = BNT
> port = /dev/ttyS1
> numOfBytesFromUPS = 16
> methodOfFlowControl = no_flow_control
> validationSequence = {{11,0x42},{8,0},{8,0}}
> shutdownArguments = {{1,30},y}
> modelname = BNT2000APT
> serialnumber = 2233445566
> Desc = Computer Room Small UPS
>
> So, the "numOfBytesFromUPS", "methodOfFlowControl",
> "validationSequence", and "shutdownArguments" are all defaults for
> "BNT" and can be commented out of the config file. You can also let
> NUT attempt to figure it all out by commenting out the "type" as well.
This I did with the settings below!
> However, I would simplify the config file as follows:
> >> > > [APC1]
> >> > >
> >> > > driver = powercom
> >> > > port = /dev/ttyS1
> >> > > modelname = BNT2000APT
> >> > > serialnumber = 2233445566
> >> > > desc = Computer Room Small UPS
Result was worse with only 11 bytes!
> and then, if that doesn't give you what you need, add "type =
> BNT-other", repeat test, and add other elements as needed until you
> get what you want.
> Using "BNT-other", you can tweak all the settings to what you need for
> display. The defaults for "BNT-other" will choose between BNT, KIN,
> and IMP based on raw values. Especially, if you have a 120 volt (US)
> model, use "BNT-other" or set "linevoltage = 240". I use KNutClient to
> check that my values are being reported accurately and tweak them
> until they are correct (assuming there isn't a problem with the UPS).
> An example "BNT-other" config:
>
> [BNT1500AP]
> driver = powercom
> port = /dev/ttyS0
> desc = "PowerCom BNT 1500 AP"
> manufacturer = PowerCom
> modelname = BNT1500AP
> serialnumber = 13245678900
> type = BNT-other
> # linevoltage = 120
> # numOfBytesFromUPS = 16
> # methodOfFlowControl = no_flow_control
> # validationSequence = {{8,0},{8,0},{8,0}}
> # shutdownArguments = {{1,30},y}
> # frequency = {0.00027778,0.0000}
> # loadPercentage = {1.0000,0.0,1.0000,0.0}
> # batteryPercentage = {1.0000,0.0000,0.0000,1.0000,0.0000}
> # voltage = {2.0000,0.0000,2.0000,0.0000}
I just added the type as suggest of BNT-other and would you believe that it
worked!
Here is the debug output!
gatekeeper nut # /lib/nut/powercom -a APC1 -DDDDDDDDDD
Network UPS Tools - PowerCom protocol UPS driver 0.13 (2.6.0-r2984)
0.000000 debug level is '10'
0.001862 Flow control disable
0.002045 Num of bytes requested for reading from UPS: 16
0.147783 Num of bytes received from UPS: 16
Raw data from UPS:
0 0x0f ( )
1 0x64 (d)
2 0x70 (p)
3 0x70 (p)
4 0x32 (2)
5 0xff (ÿ)
6 0x32 (2)
7 0x00 ( )
8 0x00 ( )
9 0x04 ( )
10 0x00 ( )
11 0x4b (K)
12 0x98 ()
13 0x00 ( )
14 0x00 ( )
15 0x00 ( )
0.147958 Detected: BNT-other-2000AP , 220V
0.148042 Values of arguments:
0.148065 manufacturer : 'PowerCom'
0.148085 model name : 'BNT2000APT'
0.148105 serial number : '2233445566'
0.148125 line voltage : '220'
0.148144 type : 'BNT-other'
0.148164 number of bytes from UPS: '16'
0.148183 method of flow control : 'no_flow_control'
0.148206 validation sequence: '{{8,0},{8,0},{8,0}}'
0.148227 shutdown arguments: '{{1,30},y}'
0.148264 frequency calculation coefficients: '{0.000278,0.000000}'
0.148292 load percentage calculation coefficients:
'{1.000000,0.000000,1.000000,0.000000}'
0.148321 battery percentage calculation coefficients:
'{1.000000,0.000000,0.000000,1.000000,0.000000}'
0.148345 voltage calculation coefficients: '{2.000000,0.000000}'
0.148387 send_to_all: SETINFO device.type "ups"
0.148415 send_to_all: SETINFO driver.version "2.6.0-r2984"
0.148442 send_to_all: SETINFO driver.version.internal "0.13"
0.148469 send_to_all: SETINFO driver.name "powercom"
0.148497 send_to_all: SETINFO ups.mfr "PowerCom"
0.148523 send_to_all: SETINFO ups.model "BNT2000APT"
0.148550 send_to_all: SETINFO ups.serial "2233445566"
0.148576 send_to_all: SETINFO ups.model.type "BNT-other"
0.148603 send_to_all: SETINFO input.voltage.nominal "220"
0.148628 send_to_all: ADDCMD test.battery.start
0.148650 send_to_all: ADDCMD shutdown.return
0.148673 send_to_all: ADDCMD shutdown.stayoff
0.148811 Num of bytes requested for reading from UPS: 16
0.301784 Num of bytes received from UPS: 16
Raw data from UPS:
0 0x0e ( )
1 0x64 (d)
2 0x70 (p)
3 0x70 (p)
4 0x32 (2)
5 0xff (ÿ)
6 0x32 (2)
7 0x00 ( )
8 0x00 ( )
9 0x01 ( )
10 0x04 ( )
11 0x4b (K)
12 0x98 ()
13 0x00 ( )
14 0x00 ( )
15 0x00 ( )
0.301948 input.frequency (raw data): [raw: 50]
0.301996 send_to_all: SETINFO input.frequency "72.00"
0.302020 input.frequency: 72.00
0.302040 output.frequency (raw data): [raw: 50]
0.302070 send_to_all: SETINFO output.frequency "72.00"
0.302091 output.frequency: 72.00
0.302110 ups.load (raw data): [raw: 14]
0.302140 send_to_all: SETINFO ups.load "14.0"
0.302161 ups.load: 14.0
0.302180 battery.charge (raw data): [raw: 100]
0.302211 send_to_all: SETINFO battery.charge "100.0"
0.302232 battery.charge: 100.0
0.302251 input.voltage (raw data): [raw: 112]
0.302281 send_to_all: SETINFO input.voltage "224.0"
0.302303 input.voltage: 224.0
0.302322 output.voltage (raw data): [raw: 112]
0.302352 send_to_all: SETINFO output.voltage "224.0"
0.302373 output.voltage: 224.0
0.302403 send_to_all: SETINFO ups.status "OB TEST"
0.302425 STATUS: OB TEST
0.302445 send_to_all: DATAOK
0.302723 dstate_init: sock /var/lib/nut/powercom-APC1 open on fd 5
0.302833 send_to_all: SETINFO driver.parameter.pollinterval "2"
0.302872 send_to_all: SETINFO device.mfr "PowerCom"
0.302900 send_to_all: SETINFO device.model "BNT2000APT"
0.302928 send_to_all: SETINFO device.serial "2233445566"
> I hope that clears up any problems,
It certainly seems to have! If you want me to try anything else give me a
shout! I'm sure my customer will be happier that the firewall/front-end mail-
server will be shudown on a power outage! They are in a sightly rural
industrial area. Power demands is at the supply capability level. But then
that's quite common here in South Africa at the moment! We are expecting
rolling blackouts again this winter until the new power stations come on line!
2012 and onwards should see things improve!