[Nut-upsuser] Differences between USB and serial on an MGE Pulsar Evolution 3000
    Neil A. Hillard 
    neil at dana.org.uk
       
    Thu Oct  6 15:05:23 UTC 2011
    
    
  
Hi Arnaud,
Many thanks for your quick reply.
>> Unfortunately there appears to be a lot of parameters missing from the
>> serial driver (using mge-shut) when compared to the USB driver (usbhid-ups)
>> and more importantly, output.voltage.nominal is reported at 72 Volts instead
>> of the correct 230 Volts.
<snip>
> I won't go in depth, but this is a known point:
> http://bugs.debian.org/cgi-bin/bugreport.cgi?bug=411864
Many thanks for the pointer.  Don't know how I managed to miss that 
during my searching but that details my experiences, too.
> This is also why I've developed the 'newmge-shut' driver, which shares
> a lot of code with the usbhid-ups one.
> FYI, SHUT stands for Serial HID UPS Transfer, which is basically HID
> (as in USB, so the same data) but over a serial link.
>
> the newmge-shut take over has been postponed for some time, but it's
> only due to a lack of time and formal testing, more than issues with
> this driver. And mge-shut is not really maintained anymore...
>
> could you please test again with newmge-shut, and report back?
I actually noticed newmge-shut just after I sent my original message so 
I've got the upsc output handy (listed below).  I've highlighted the 
values that differ from the USB output (with an asterisk) and I've 
spotted that there are a few parameters missing:
input.frequency.extended
input.frequency.nominal
input.voltage.extended
ups.beeper.status
ups.test.result
If there's anything I can do to help get these added or perform some 
more testing then please let me know.
Many thanks once again,
Neil.
newmge-shut output
------------------
battery.charge: 100
*battery.charge.low: 100
*battery.charge.restart: 100
battery.energysave: no
*battery.protection: no
battery.runtime: 5400
battery.type: PbAc
device.mfr: MGE UPS SYSTEMS
device.model: Pulsar Evolution 3000
device.serial: AF3E39202
device.type: ups
driver.name: newmge-shut
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ups0
driver.version: 2.6.2
driver.version.data: MGE HID 1.27
driver.version.internal: 0.35
input.frequency: 50.0
*input.frequency.nominal: 230
input.transfer.boost.low: 184
input.transfer.high: 294
input.transfer.low: 160
input.transfer.trim.high: 265
input.voltage: 237.0
input.voltage.nominal: 230
*outlet.1.autoswitch.charge.low: 1
outlet.1.delay.shutdown: 65535
outlet.1.delay.start: 3
outlet.1.desc: PowerShare Outlet 1
outlet.1.id: 1
outlet.1.status: on
outlet.1.switchable: yes
*outlet.2.autoswitch.charge.low: 3
outlet.2.delay.shutdown: 65535
outlet.2.delay.start: 6
outlet.2.desc: PowerShare Outlet 2
outlet.2.id: 2
outlet.2.status: on
outlet.2.switchable: yes
outlet.desc: Main Outlet
outlet.id: 0
outlet.switchable: no
output.current: 1.00
output.current.nominal: 13.04
output.frequency: 50.0
*output.frequency.nominal: 24
output.voltage: 236.0
output.voltage.nominal: 230
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 10
ups.mfr: MGE UPS SYSTEMS
ups.model: Pulsar Evolution 3000
ups.power: 210
ups.power.nominal: 3000
ups.productid: ffff
ups.realpower.nominal: 2000
ups.serial: AF3E39202
*ups.start.auto: no
*ups.start.battery: no
*ups.start.reboot: no
ups.status: OL CHRG
ups.test.interval: 604800
ups.timer.shutdown: -1
ups.timer.start: -10
ups.type: offline / line interactive
ups.vendorid: 0463
    
    
More information about the Nut-upsuser