[Nut-upsuser] Slaves under Squeeze
    Charles Lepple 
    clepple at gmail.com
       
    Thu Sep 15 00:14:46 UTC 2011
    
    
  
On Wed, Sep 14, 2011 at 7:57 PM, Rob Donovan <hikerman2005-nut at yahoo.com> wrote:
> hi,
>    I recently upgraded my Debian Lenny system to Squeeze, and have been
> happily running nut as a MODE=standalone system talking to my Cyberpower
> 1500 avr lcd via the usbhid-ups driver for a couple of weeks or so.  No
> problems.
>
>   Now I'm trying to hang another machine off the same ups as a slave, and it
> isn't working.  The problem I'm getting is best illustrated by what happens
> when I run this on the server:
>
> upsd -DDDDDDDDD
> Network UPS Tools upsd 2.4.3
>  0.000000     listen_add: added 127.0.0.1:3493
>  0.000070     listen_add: added 192.168.1.104:3493
>  0.000117     setuptcp: try to bind to 192.168.1.104 port 3493
>  0.000204     setuptcp: bind: Cannot assign requested address
>  0.000226     not listening on 192.168.1.104 port 3493
The short answer is that the "listen" directive specifies the address
on the *server* that will be used for listening.
I think you're trying to specify that the server should only listen to
that one slave. Those rules are best handled by the system firewall
(and/or by tcp_wrappers), which is why we dropped the ACL syntax from
NUT.
Your choices for the listen directive are basically any of the
addresses shown in 'ifconfig', or 0.0.0.0 to listen on all IPv4
interfaces.
-- 
- Charles Lepple
    
    
More information about the Nut-upsuser