Arnaud Quette wrote (2012-02-02 14:13):
I did a test with an older version of my UPS, same model, but no USB
connector. This time, everything worked fine:
Feb  4 12:01:37 b1 upsmon[1494]: UPS upsb1 at localhost on battery
Feb  4 12:18:52 b1 upsmon[1494]: UPS upsb1 at localhost battery is low
Feb  4 12:18:52 b1 upsmon[1494]: Executing automatic power-fail shutdown
Feb  4 12:18:52 b1 upsmon[1494]: Auto logout and shutdown proceeding
[...]
Feb  4 12:19:06 b1 upsd[1480]: mainloop: Interrupted system call
[...]
Feb  4 12:19:10 b1 syslogd: exiting on signal 15
> /etc/killpower is cleared at upsmon startup, in case it exists.
It was this time, but not when the shutdown had failed.
> you have not answered to my question on where "upsdrvctl shutdown" is
> called in the process?
> as told, on Debian, it's handled by the halt script.
It's in /usr/local/etc/rc.d/nut, which is called when entering shutdown
"runlevel".
I watched the upsc output during that test. It started with
ups.alarm: INPUT_AC_UNDER_VOLTAGE INPUT_UNDER_OR_OVER_FREQ
UTILITY_NOT_PRESENT BATTERY_TOTALLY_DISCHARGED LOAD_DUMPED
ups.beeper.status: enabled
ups.status: ALARM OB
I disabled the beeper with the button at the fron panel, but it still
said enabled.
The LOAD_DUMPED output is nonsense, this UPS cannot dump load (except
for dumping everything, which it didn't) and the battery was not totally
discharged when I started the test.
Later on it said:
battery.charge: 70
battery.runtime: 95
battery.voltage: 10.49
ups.alarm: INPUT_AC_UNDER_VOLTAGE INPUT_UNDER_OR_OVER_FREQ UTILITY_FAIL
UTILITY_NOT_PRESENT BATTERY_TOTALLY_DISCHARGED LOAD_DUMPED
ups.status: FSD ALARM OB LB
So finally, the utility which was not present (see above) now failed. :-)
I guess, Ill configure that timer thing, just to be sure shutdown works.
    
    