[Nut-upsuser] Support for Online Yunto and Zinto

Thomas Maisl exp-122008 at maisl.com
Mon Feb 13 17:50:10 UTC 2012


schrieb Arnaud Quette, Am 13.02.2012 18:28:
>
> for the 2nd, as per its USB IDs (06DA/0002), the driver should be bcmxcp_usb.
> can you please try it in debug more and also send back the output?
>
A few minutes ago I managed to connect to a Yunto YQ450 using USB connection.

 [YQ450]
        driver = blazer_usb
        subdriver = phoenix
        vendorid = 06da
        productid = 0002
        port = auto
        desc = "Yunto YQ450 via USB"

I'm not shure if everything (all available parameters/values) is ok. Debug
output:
>  /lib/nut/blazer_usb -a YQ450 -DDDDD
> Network UPS Tools - Megatec/Q1 protocol USB driver 0.04 (2.6.3)
>    0.000000     debug level is '5'
>    0.078276     Checking device (1D6B/0001) (004/001)
>    [..]
>    0.078745     Checking device (06DA/0002) (002/003)
>    0.098362     - VendorID: 06da
>    0.098474     - ProductID: 0002
>    0.098566     - Manufacturer: ONLINE
>    0.098617     - Product: YUNTO
>    0.098657     - Serial Number: unknown
>    0.098698     - Bus: 002
>    0.098737     Trying to match device
>    0.098903     Device matches
>    0.099009     failed to claim USB device: could not claim interface 0:
> Device or resource busy
>    0.137797     detached kernel driver from USB device...
>    0.142334     send_to_all: SETINFO ups.vendorid "06da"
>    0.142391     send_to_all: SETINFO ups.productid "0002"
>    0.142420     send_to_all: SETINFO device.type "ups"
>    0.142442     send_to_all: SETINFO driver.version "2.6.3"
>    0.142462     send_to_all: SETINFO driver.version.internal "0.04"
>    0.142483     send_to_all: SETINFO driver.name "blazer_usb"
>    0.142502     Trying megatec protocol...
>    1.145357     flush: could not claim interface 0: Device or resource busy
>    1.149216     send: Q1
>    1.527180     read: (228.0 002.0 228.0 000 49.9 13.7 25.0 00101000
>    1.527358     send_to_all: SETINFO input.voltage "228.0"
>    1.527431     send_to_all: SETINFO input.voltage.fault "2.0"
>    1.527502     send_to_all: SETINFO output.voltage "228.0"
>    1.527552     send_to_all: SETINFO ups.load "0"
>    1.527583     send_to_all: SETINFO input.frequency "49.9"
>    1.527610     send_to_all: SETINFO battery.voltage "13.70"
>    1.527634     send_to_all: SETINFO ups.temperature "25.0"
>    1.527660     send_to_all: SETINFO beeper.status "disabled"
>    1.527682     send_to_all: SETINFO ups.type "offline / line interactive"
>    1.527711     send_to_all: SETINFO ups.status "OL BYPASS"
>    1.527729     Status read in 1 tries
>    1.527746     Supported UPS detected with megatec protocol
>    2.530350     flush: could not claim interface 0: Device or resource busy
>    2.534335     send: F
>    3.537357     read: could not claim interface 0: Device or resource busy
>    3.537475     blazer_rating: short reply
>    3.537572     Rating read 1 failed
>    4.540354     flush: could not claim interface 0: Device or resource busy
>    4.544349     send: F
>    5.546183     read: could not claim interface 0: Device or resource busy
>    5.546266     blazer_rating: short reply
>    5.546309     Rating read 2 failed
>    6.549183     flush: could not claim interface 0: Device or resource busy
>    6.553248     send: F
>    7.555355     read: could not claim interface 0: Device or resource busy
>    7.555471     blazer_rating: short reply
>    7.555569     Rating read 3 failed
>    7.555614     Rating information unavailable
>    8.557177     flush: could not claim interface 0: Device or resource busy
>    8.561245     send: I
>    9.563177     read: could not claim interface 0: Device or resource busy
>    9.563262     blazer_vendor: short reply
>    9.563307     Vendor information read 1 failed
>   10.566164     flush: could not claim interface 0: Device or resource busy
>   10.570338     send: I
>   11.572352     read: could not claim interface 0: Device or resource busy
>   11.572477     blazer_vendor: short reply
>   11.572572     Vendor information read 2 failed
>   12.574358     flush: could not claim interface 0: Device or resource busy
>   12.578335     send: I
>   13.581180     read: could not claim interface 0: Device or resource busy
>   13.581267     blazer_vendor: short reply
>   13.581314     Vendor information read 3 failed
>   13.581354     Vendor information unavailable
>   13.581395     Battery runtime will not be calculated (runtimecal not set)
>   13.581445     send_to_all: SETINFO ups.delay.start "180"
>   13.581468     send_to_all: SETINFO ups.delay.shutdown "30"
>   13.581488     send_to_all: ADDCMD beeper.toggle
>   13.581507     send_to_all: ADDCMD load.off
>   13.581525     send_to_all: ADDCMD load.on
>   13.581543     send_to_all: ADDCMD shutdown.return
>   13.581562     send_to_all: ADDCMD shutdown.stayoff
>   13.581581     send_to_all: ADDCMD shutdown.stop
>   13.581599     send_to_all: ADDCMD test.battery.start
>   13.581618     send_to_all: ADDCMD test.battery.start.deep
>   13.581637     send_to_all: ADDCMD test.battery.start.quick
>   13.581657     send_to_all: ADDCMD test.battery.stop
>   14.583159     flush: could not claim interface 0: Device or resource busy
>   14.587338     send: Q1
>   14.967370     read: (228.0 002.0 228.0 000 49.9 13.7 25.0 00101000
>   14.967627     send_to_all: DATAOK
>   14.967931     dstate_init: sock /var/run/nut/blazer_usb-YQ450 open on fd 5
>   14.968022     send_to_all: SETINFO driver.parameter.pollinterval "2"
>   15.970186     flush: could not claim interface 0: Device or resource busy
>   15.974166     send: Q1
>   16.343393     read: (228.0 002.0 228.0 000 49.9 13.7 25.0 00101000
>   16.822141     new connection on fd 6
>   16.822543     send_to_one: SETINFO battery.voltage "13.70"
>   16.822622     send_to_one: SETINFO beeper.status "disabled"
>   16.822647     send_to_one: SETINFO device.type "ups"
>   16.822669     send_to_one: SETINFO driver.name "blazer_usb"
>   16.822691     send_to_one: SETINFO driver.parameter.pollinterval "2"
>   16.822714     send_to_one: SETINFO driver.parameter.port "auto"
>   16.822737     send_to_one: SETINFO driver.parameter.productid "0002"
>   16.822759     send_to_one: SETINFO driver.parameter.subdriver "phoenix"
>   16.822782     send_to_one: SETINFO driver.parameter.vendorid "06da"
>   16.822804     send_to_one: SETINFO driver.version "2.6.3"
>   16.822826     send_to_one: SETINFO driver.version.internal "0.04"
>   16.822848     send_to_one: SETINFO input.frequency "49.9"
>   16.822872     send_to_one: SETINFO input.voltage "228.0"
>   16.822895     send_to_one: SETINFO input.voltage.fault "2.0"
>   16.822917     send_to_one: SETINFO output.voltage "228.0"
>   16.822941     send_to_one: SETINFO ups.delay.shutdown "30"
>   16.822964     send_to_one: SETINFO ups.delay.start "180"
>   16.822987     send_to_one: SETINFO ups.load "0"
>   16.823009     send_to_one: SETINFO ups.productid "0002"
>   16.823031     send_to_one: SETINFO ups.status "OL BYPASS"
>   16.823053     send_to_one: SETINFO ups.temperature "25.0"
>   16.823075     send_to_one: SETINFO ups.type "offline / line interactive"
>   16.823097     send_to_one: SETINFO ups.vendorid "06da"
>   16.823119     send_to_one: ADDCMD beeper.toggle
>   16.823141     send_to_one: ADDCMD load.off
>   16.823162     send_to_one: ADDCMD load.on
>   16.823183     send_to_one: ADDCMD shutdown.return
>   16.823204     send_to_one: ADDCMD shutdown.stayoff
>   16.823225     send_to_one: ADDCMD shutdown.stop
>   16.823246     send_to_one: ADDCMD test.battery.start
>   16.823267     send_to_one: ADDCMD test.battery.start.deep
>   16.823296     send_to_one: ADDCMD test.battery.start.quick
>   16.823317     send_to_one: ADDCMD test.battery.stop
>   16.823338     send_to_one: DATAOK
>   16.823358     send_to_one: DUMPDONE
>   17.970353     flush: could not claim interface 0: Device or resource busy
>   17.974263     send: Q1
>   18.327183     read: (228.0 002.0 228.0 000 49.9 13.7 25.0 00101000
>   19.971366     flush: could not claim interface 0: Device or resource busy
>   19.975352     send: Q1
>   20.343369     read: (229.0 002.0 228.0 000 49.9 13.7 25.0 00101000
>   20.343566     send_to_all: SETINFO input.voltage "229.0"
>   21.972355     flush: could not claim interface 0: Device or resource busy
>   21.976359     send: Q1
>   22.327184     read: (228.0 002.0 228.0 000 49.9 13.7 25.0 00101000
>   22.327299     send_to_all: SETINFO input.voltage "228.0"
>   23.973360     flush: could not claim interface 0: Device or resource busy
>   23.977250     send: Q1
>   24.343179     read: (228.0 002.0 228.0 000 49.9 13.7 25.0 00101000
>   25.974238     flush: could not claim interface 0: Device or resource busy
>   25.978338     send: Q1
>   26.327194     read: (229.0 002.0 228.0 000 49.9 13.7 25.0 00101000
>   26.327308     send_to_all: SETINFO input.voltage "229.0"
>   27.974357     flush: could not claim interface 0: Device or resource busy
>   27.978339     send: Q1
>   28.343184     read: (228.0 002.0 228.0 000 49.9 13.7 25.0 00101000
>   28.343296     send_to_all: SETINFO input.voltage "228.0"
>   29.975356     flush: could not claim interface 0: Device or resource busy
>   29.979339     send: Q1
>   30.359372     read: (228.0 002.0 228.0 000 49.9 13.7 25.0 00101000
>   31.976356     flush: could not claim interface 0: Device or resource busy
>   31.980382     send: Q1