[Nut-upsuser] Support for Online Yunto and Zinto
Arnaud Quette
aquette.dev at gmail.com
Tue Feb 28 17:51:13 UTC 2012
2012/2/27 Thomas Maisl <exp-122008 at maisl.com>:
> Hello,
>
> schrieb Arnaud Quette, Am 16.02.2012 18:48:
>
>> Can you please counter check, and report back upsc/upsrw/upscmd
>
> upsc:
> # upsc YQ450
> battery.voltage: 13.40
> beeper.status: disabled
> device.type: ups
> driver.name: blazer_usb
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.parameter.productid: 0002
> driver.parameter.protocol: zinto
> driver.parameter.subdriver: cypress
> driver.parameter.vendorid: 06da
> driver.version: 2.6.3
> driver.version.internal: 0.04
> input.frequency: 50.0
> input.voltage: 232.0
> input.voltage.fault: 1.0
this seems not normal!
> output.voltage: 232.0
> ups.delay.shutdown: 30
> ups.delay.start: 180
> ups.load: 0
> ups.productid: 0002
> ups.status: OL BYPASS
> ups.temperature: 25.0
> ups.type: offline / line interactive
> ups.vendorid: 06da
>
> # upsrw -u xxx -p xxx -s ups.delay.start YQ450
> Enter new value for ups.delay.start: 90
> Unexpected response from upsd: ERR ACCESS-DENIED
> # upsrw -u xxx -p xxx -s ups.delay.shutdown YQ450
> Enter new value for ups.delay.shutdown: 90
> Unexpected response from upsd: ERR ACCESS-DENIED
>
> # upscmd -u xxx -p xxx YQ450 shutdown.return 1
> Unexpected response from upsd: ERR ACCESS-DENIED
the user and password used for upsrw and upscmd are the ones defined
in upsd.users.
here, upsd is telling us that you've used wrong ones (generally system
ones, such as root...).
>> output, along with the shutdown test:
>> http://www.networkupstools.org/docs/user-manual.chunked/ar01s06.html#Shutdown_design
>>
>
> while doing shutdown
> # upslog -s yq450 -i 2 -l -
> Network UPS Tools upslog 2.6.3
> logging status of yq450 to - (2s intervals)
> 20120227 091805 NA 0.0 0 [OB] 25.0 0.0
> 20120227 091807 NA 0.0 0 [OB] 25.0 0.0
> 20120227 091809 NA 0.0 0 [OB] 25.0 0.0
> 20120227 091811 NA 0.0 0 [OB] 25.0 0.0
> 20120227 091957 NA NA NA [FSD WAIT] NA 0.0
> 20120227 091959 NA 0.0 0 [FSD OB] 25.0 0.0
> 20120227 092001 NA 0.0 0 [FSD OB LB] 25.0 0.0
> 20120227 092003 NA 0.0 0 [FSD OB LB] 25.0 0.0
> so, no battery voltage is displayed
battery.voltage is not part of the default upslog string:
%TIME @Y at m@d @H at M@S% %VAR battery.charge% %VAR input.voltage% %VAR
ups.load% [%VAR ups.status%] %VAR ups.temperature% %VAR
input.frequency%
the above shows that OB+LB has triggered FSD.
so upsmon.conf->SHUTDOWNCMD has been executed.
> parallel
> /lib/nut/blazer_usb -a YQ450 -DDDDD
> 23.832061 read: (000.0 001.0 230.0 000 00.0 12.5 25.0 10001000
> 25.472224 send: Q1
> 25.816057 read: (000.0 001.0 230.0 000 00.0 12.5 25.0 11001000
> 25.816249 send_to_all: SETINFO ups.status "OB LB"
> 27.473243 send: Q1
> 27.832053 read: (000.0 001.0 230.0 000 00.0 12.5 25.0 11001000
> 29.476227 send: Q1
> 29.848055 read: (000.0 001.0 230.0 000 00.0 12.5 25.0 11001000
> 31.478227 send: Q1
> 31.832056 read: (000.0 001.0 230.0 000 00.0 12.5 25.0 11001000
> 32.070549 send_to_one: PONG
>
> Temperature is always 25.0°C
> When cutting off power to the UPS, power to the outlets isn't switched off
> despite the low battery warning (at least 15 minutes after cutting power)
> Do I have a faulty UPS?2
it depends on what you mean with "cutting off power to the UPS"...
if you refer to "upscmd -u xxx -p xxx YQ450 shutdown.return", it has failed.
if you mean following the above FSD, it's indeed not normal.
I would need the driver output when going FSD (or using "upscmd...
shutdown.return")
remember to not power your PC with the UPS while testing this!
note that you may also contact the manufacturer support to get some
help on their possible variation of the protocol.
cheers,
Arno
More information about the Nut-upsuser
mailing list