On 21/07/2012, at 22:55, Charles Lepple wrote:
>> Does anyone know if this is possible? A setting like this would provide some hysteresis for successive power failures which would be handy to have :)
> 
> I don't know about that specific hardware, but the variables which would control this are battery.charge.restart ("Minimum battery level for UPS restart after power-off") and ups.delay.start ("Interval to wait before restarting the load (seconds)"). Check the output of "upsrw <ups>" to see if that variable is supported with your combination of UPS and driver.
> 
> Which version of NUT are you using? There might be a newmge-shut driver included as well.

I tried mge-shut in 2.6 with no change, but newmge-shut with 2.6 showed this parameter, thanks!

--