[Nut-upsuser] NUT 2.6.3, openSUSE 12.2 : UPS unit not switched off: Fixed
Arnaud Quette
aquette.dev at gmail.com
Mon Oct 29 20:17:31 UTC 2012
Hi Roger,
note that I'm cc'ing Stanislav (maintainer of the NUT packages in Suse).
thanks for Kris Jordan for the support interim too ;)
2012/10/28 Roger Price <roger at rogerprice.org>
> On Fri, 26 Oct 2012, Kris Jordan wrote:
>
>> Did you install NUT from a package? Note, 2.6.5 is the current
>> version and 2.6.4 had fixed a vulnerability.
>>
>
> I'm using the nut 2.6.3 package included in the openSUSE 12.2 distribution.
>
> Check that your distribution's shutdown script is running 'upsdrvctl
>> shutdown' in the presence of the killpower file
>> (POWERDOWNFLAG).
>>
>
> Summary: looks like an openSUSE bug, simple fix available.
>
> OpenSUSE 12.2 has a script /usr/sbin/rcupsd for starting and stopping the
> upsd service. This is a link to script /etc/init.d/upsd which contains:
>
> powerdown)
> ## Special command: Instruct UPS to shutdown.
> sync &
> if grep -q '^\[' $UPS_CONFIG ; then
> echo -n "Instructing UPS to powerdown "
> $UPSDRVCTL_BIN shutdown >/dev/null 2>&1 || rc_failed
> rc_check
> else
> echo "No local UPS defined, skipping powerdown "
> fi
> rc_status -v
> ;;
> try-powerdown)
> ## Special command: Instruct UPS to shutdown, if halt is running
> ## or variable UPSD_POWERDOWN_CONDITION is set and power is
> failing.
> ## Otherwise silently quit.
> ##
> if test "$RUNLEVEL" = "0" -o -n "$UPSD_POWERDOWN_CONDITION" ; then
> if test -n "$POWERDOWNFLAG" -a -f "$POWERDOWNFLAG" ; then
> exec $0 powerdown
> fi
> fi
> ;;
>
> where UPSDRVCTL_BIN=/usr/lib/ups/**driver/upsdrvctl
>
> In addition, file /etc/sysconfig/shutdown contains the configuration
> parameter
>
> # Hook during system shutdown to run extra command
> HALT_POWERDOWN_INSERT="/etc/**init.d/upsd try-powerdown"
>
> but when upsd try-powerdown is called it fails silently because $RUNLEVEL
> and $UPSD_POWERDOWN_CONDITION are empty. upsd powerdown is never called.
>
> I changed the configuration parameter to HALT_POWERDOWN_INSERT="/etc/**init.d/upsd
> powerdown", reran command SuSEconfig, and tried again but there was no
> change. However typing the command /etc/init.d/upsd powerdown does shut
> down the UPS unit.
>
> OpenSUSE 12.2 has fully embraced systemctl and systemd: I tried grepping
> around in the /lib/systemd shutdown specifications, but I cannot find any
> reference to /etc/init.d/upsd powerdown. This is beginning to look like a
> bug in openSUSE 12.2 which I will report in their forums.
>
> Here is a fix: There is a file /etc/init.d/halt.local which is currently
> empty:
>
> # /etc/init.d/halt.local
> # script with local commands to be executed from init on system shutdown
> # Here you should add things, that should happen directly before shuting
> # down.
>
> I added the lines
>
> # RP 2012-10-28 Turn off the UPS unit.
> # Needed for automatic system restart when wall power returns.
> UPSDRVCTL_BIN=/usr/lib/ups/**driver/upsdrvctl
> echo `date -I` `date +%T` "$0 calls $UPSDRVCTL_BIN shutdown" >>
> /var/log/halt.local
> $UPSDRVCTL_BIN shutdown
>
> I pulled the plug from the wall and witnessed a server shutdown followed
> 10 seconds later by a UPS shutdown. Pushing the plug back into the wall
> got the system running again.
>
I just saw that you (Roger) had a parallel discussion on Suse forums,
possibly leading toward some systemd integration issue...
maybe Stan can shed some light on this.
cheers,
Arnaud
--
Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org
Debian Developer - http://www.debian.org
Free Software Developer - http://arnaud.quette.fr