[Nut-upsuser] Communications with UPS lost: No status from UPS

Arnaud Quette aquette.dev at gmail.com
Fri Sep 7 15:15:49 UTC 2012


2012/9/6 Fabio Cecamore <ceca_89 at hotmail.com>

>   Updated to the last (in the testing debian repository) available: 2.6.4
> This time using blazer_ser in debug i find:
>
> 363.373978    read: '(233.9 140.0 233.9 006 49.8 13.7 30.7 00001001'
> 365.162745    send: 'Q1'
> 366.163904    read: timeout
> 366.163991    blazer_status: short reply
> 366.164013    Communications with UPS lost: status read failed!
> 367.163804    send: 'Q1'
> 367.378009    read: '(234.3 140.0 234.3 006 49.4 13.7 30.7 00001001'
>
> But this time in syslogd.log no error.. i’ll check more and will let you
> know.
>

so the expected behavior is fine? (to be confirmed)


> (nice to see an other android user)
>

they are everywhere ;)

cheers,
Arnaud
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20120907/5b3d6505/attachment.html>


More information about the Nut-upsuser mailing list