On Dec 7, 2013, at 12:06 AM, Kris Jordan wrote:
> apcsmart quick power cuts @ 20 & 30
> usbhid-ups @ 30 & 40
>
> The APC unit logs alert_handler: OB. usbhid-ups isn't so obvious, so I'm not sure.
$ grep send_to_all usbhid-ups.log|grep ups.status
10.538414 send_to_all: SETINFO ups.status "OL CHRG"
30.912005 send_to_all: SETINFO ups.status "OB DISCHRG"
32.585047 send_to_all: SETINFO ups.status "OL CHRG"
40.667472 send_to_all: SETINFO ups.status "OB DISCHRG"
43.223281 send_to_all: SETINFO ups.status "OL CHRG"
> At least the apcsmart driver is reacting immediately, but upsmon reports nothing unless I cut power long enough. upsmond has noticed quick power cut, but I think that's because It happened at the same time as the normal check interval. I'm using defaults here, as far as poll intervals.
>
> Maybe upsd is getting the message, does it push upsmon?
Good point. It's polling, at a default interval of 5 seconds:
https://github.com/networkupstools/nut/blob/v2.7.1/clients/upsmon.c#L2010
Adding something like the IMAP IDLE command to the NUT protocol should enable pushing messages, but would require the client polling loops to be reworked. In the short term, decreasing the upsmon.conf POLLFREQ and POLLFREQALERT settings should catch the shorter events.
> I thought to try upsd at full debugging to see if it says anything, but it appears that nothing special is shown for UPS/driver events.
I added the upsd case to https://github.com/networkupstools/nut/issues/79
--
Charles Lepple
clepple at gmail
More information about the Nut-upsuser