[Nut-upsuser] APC Smart-UPS 1500; system shutdown is not initiated.
Christian
chanlists at googlemail.com
Tue Dec 17 11:10:28 UTC 2013
Charles,
the unit has two redundant power supplies, with only one hooked up to
the UPS. So I should be able to do a deep test with the machine itself,
right? I have tried it, but it aborts at some point...
For the quick test, it discharges the battery a bit, then recharges, but
once it is back to 100%, upsc still gives me:
ups.test.result: No test initiated
Is that expected?
Best,
Christian
Am 17.12.2013 03:55, schrieb Charles Lepple:
> On Dec 8, 2013, at 10:41 PM, Christian wrote:
>
>> test.battery.start.deep - Start a deep battery test
>> test.battery.start.quick - Start a quick battery test
>
> Ideally, you would want to do a deep test with a dummy load, like a
> lamp, so as not to put your server in danger of getting cut off
> again. You can probably do the test.battery.start.quick test with
> the server still plugged into the UPS, though.
>