On Aug 7, 2014, at 10:52 PM, Charles Lepple <clepple at gmail.com> wrote:
> On Aug 7, 2014, at 10:18 PM, Matthew Stapleton <matthew4196 at gmail.com> wrote:
>
>> I just got a Cyberpower SOHO Value 1200 ELCD UPS and even with nut 2.7.2, it appears to report battery voltage too low due to the battery scaling function (In drivers/cps-hid.c). Even though the ups has usb id: 0764:0501, UPS.PowerSummary.Voltage reports 26.6 for the 24V batteries so when the 0.667 battery scale is applied that goes down to 17.7V.
>
> I'm wondering if that scale factor is only needed for that one Dynex UPS model. We should be able to do a string match, which is ugly, but should work (especially if we default to no scaling).
>
> Logged: https://github.com/networkupstools/nut/issues/142
It's not just Dynex models - there are some early "UPS VALUE" and "CP 1000D" units that seem to need the correction factor. I'll try to add a check that looks to see if the battery voltage makes sense.
--