On Dec 1, 2014, at 4:11 AM, Victor Porton <porton at narod.ru> wrote:
> battery.voltage: 13.70
> battery.voltage.high: 13.00
> battery.voltage.low: 10.40
These are the voltage thresholds for the UPS, so theoretically the UPS will send the LB signal when the battery voltage goes lower than 10.40 Volts.
Also, if battery.charge works, you can use "ignorelb" if you want to shut down at another level of charge:
http://www.networkupstools.org/docs/man/ups.conf.html#_ups_fields
> ups.delay.shutdown: 30
> ups.delay.start: 180
These timers are in seconds. You will want to verify this, but according to those values, the UPS will shut off its output 30 seconds after the shutdown signal (so you need to make sure that your OS shutdown takes less time than that).
Does "upsrw -l advice" show anything?
--