[Nut-upsuser] Powerware (Eaton) Prestige 9 UPS
Tim Dawson
tadawson at tpcsvc.com
Sun Feb 2 21:40:46 UTC 2014
I noted some correspondence from several years back about supporting
this device with bcmxcp, and the problems therein. Since I have one of
these UPS units, still going strong, and the Eaton LanSafe stuff has
finally caused me enough grief to abandon it, I figured I'd take a look
at this.
The issue is not that bad - the bcmxcp driver query of the topology
block (2 bytes!) is returning as block 0x09 and not 0x13 . . . as per
the protocol spec, "some command queries may return 0x9 even if that was
not the query made" or some such verbage.
So, I made a change to bcmxcp_ser.c to handle block 0x43 a tad
differently. And after this, all works - the topology *IS* correctly
detected, all meters and functions show, it's golden . . . It just
appears that in the firmware on this thing, that the reply to query 0x43
is a bit odd, and the authors of the initial code took far too sever an
error handling path.
So, if anyone is still trying, this should get you going . . .
- Tim
-- /* if (command <= 0x43) { */
if (command << 0x43) {
if ((command - 0x30) != block_number){
ser_comm_fail("Receive error (Request
command):
%x!!!\n", block_number);
return -1;
}
}
/* Dawson - Powerware Prestige is an odd reply to topology_init . . .
but works!
Fool it into thinking it got the correct block . . . 0x13, when 0x9 is
actually returned. Maintain valid checks on all other queries.
2/2/2014 */
if (command == 0x43) {
if ((command - 0x30) != 0x13){
ser_comm_fail("Receive error (Request comm
and): %x!!!\n", block_number);
return -1;
}
}
================================================================================
Tim Dawson (tadawson at tpcsvc.com) Owner/Engineer
TPC Services Bellnet: (972)-221-7385
Lewisville, Texas 75067
"Gaff Tape can't fix 'Stupid', but it can muffle the sound..."