[Nut-upsuser] Tripplite UPS (SU10KRT3/1X) through snmp-ups (nut 2.6.5)

Charles Lepple clepple at gmail.com
Fri Feb 14 14:26:18 UTC 2014


On Feb 13, 2014, at 10:49 PM, Иши Кылса wrote:

> Slightly changed the list, took from running snmptranslate for all parameters:
> snmptranslate -IR -On upsBaseIdentModel upsBaseBatteryStatus upsSmartBatteryCapacity upsSmartBatteryTemperature upsSmartInputLineVoltage upsBaseOutputStatus upsSmartOutputVoltage upsSmartOutputFrequency upsSmartOutputLoad upsSmartControlUpsOff upsSmartControlSimulatePowerFail upsSmartControlFlashAndBeep

All but the last three are mapped here: https://github.com/networkupstools/nut/tree/snmp_subdriver @ ab7b0452e (might need to re-clone this; I rebased this on master.)

I haven't read up on the difference between NUT variables and commands in snmp-ups.

Please try building snmp-ups, and let me know how the output of upsc looks.

> .1.3.6.1.4.1.935.1.1.1.6.2.1
> .1.3.6.1.4.1.935.1.1.1.6.2.4
> .1.3.6.1.4.1.935.1.1.1.6.2.5   (Last 3 OIDs didn't return values with snmpget, all others returned correct values as listed above.)

The upsSmartControl* OIDs are probably write-only (although the MIB indicates you should be able to read them back).

-- 
Charles Lepple
clepple at gmail



-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20140214/031e9cbf/attachment.html>