[Nut-upsuser] Install problems (group permissions) with nut 2.7.2

Charles Lepple clepple at gmail.com
Thu Feb 19 01:11:13 UTC 2015


On Feb 18, 2015, at 10:40 AM, Rob Groner <rgroner at RTD.com> wrote:

> Does this revolve around hotplug and udev?

Yes. (Well, technically hotplug was superseded by udev)

>  In other words, is the idea that the created USB device will be in the "nut" group,

Yes. 

> and thus I'd be able to tell upsdrvctrl to start if I am user "ups"?   Or do ups/nut not really play into any of this?

The usual startup procedure is to run upsdrvctl as root (such as in a login script). It will automatically drop the driver to ups/nut. 

However, as you mentioned, that requires udev. I don't have an opensuse system, and the broadband connection is down, so I'm not exactly sure what you need to do there. On recent Debian and Ubuntu with 2.7.2 and earlier, there was an issue where the udev rules file needed to be renamed from 62-nut* to 52-nut* in order to not be overridden by another set of rules. It lives somewhere like /lib/udev/rules.d