On May 20, 2016, at 11:02 AM, Cédric Lemarchand wrote:
>
> I begin to suspect that the snmp driver or MIB didn’t get the change, is it possible ? or could it only be the UPS itself (snmp bug or configuration issue) ?
I am not as familiar with SNMP, so this might require some adjustment, but what happens if you run the following commands?
snmpget -v2c -c public 192.168.99.60 1.3.6.1.2.1.33.1.2.1.0 1.3.6.1.2.1.33.1.4.1.0
The first value can be interpreted with the following table:
static info_lkp_t ietf_battery_info[] = {
{ 1, "" /* unknown */ },
{ 2, "" /* batteryNormal */},
{ 3, "LB" /* batteryLow */ },
{ 4, "LB" /* batteryDepleted */ },
{ 0, NULL }
};
Similarly for the second value:
static info_lkp_t ietf_power_source_info[] = {
{ 1, "" /* other */ },
{ 2, "OFF" /* none */ },
{ 3, "OL" /* normal */ },
{ 4, "OL BYPASS" /* bypass */ },
{ 5, "OB" /* battery */ },
{ 6, "OL BOOST" /* booster */ },
{ 7, "OL TRIM" /* reducer */ },
{ 0, NULL }
};
Reference: https://github.com/networkupstools/nut/blob/master/drivers/ietf-mib.c#L38
If these values don't change when the power state changes, then the problem is upstream of NUT.
--
Charles Lepple