[Nut-upsuser] Apple Mac slave
Robbie van der Walle
rvanderwalle at gmail.com
Thu Jun 8 20:06:07 UTC 2017
> When you carry out tests to ensure that the setup is working well, you will pull the power cord from the wall and wait until the UPS reaches LB. This means waiting and wasting time. You can speed up the testing by setting LB very high so that the UPS reaches it quickly. Later you can set a more reasonable value.
After the first test and the NAS is restarted I had to change the setting battery.charge.low again to 80
> On most UPS units, there is a light which goes out. Some produce an audible clunk as the relays disconnect the UPS power outlets. You could also connect a light bulb to a protected outlet. It should go out when the UPS shuts down.
The APC produced an audible clunk. So the UPS was shutdown. I am not sure it was after 20 seconds. I have to clock that.
> Example test:
>
> 1. Pull power cord from wall
>
> 2. UPS beeps, NAS and Mac continue operation
>
> 3. Users are warned that power has failed
>
> 4. When the battery drops to battery.charge.low the slave (Mac) and then the master (NAS) shutdown.
>
> 5. After 20 seconds the UPS shuts down.
>
> 6. Reconnect the wall power
>
> 7. NAS and Mac should restart
Result test 1
1. Pull power cord from wall. — OK
2. UPS beeps, NAS and Mac continue operation
3. Users from the NAS are warned, not yet the Mac user. Only when executing automatic power-fail shutdown.
4. Yes, Both the Mac and NAS shutdown. Only the Mac shutdown so fast that it looks like pressing the off button. The NAS I have to check if it was in safe-mode some how.
5. The UPS shuts down. I heard an audible clunk.
6. Reconnect the wall power — OK
7. No they didn’t restart. I know there is a setting on the NAS to activate this. I will check and try again.
This is what is reported from the terminal on the Mac:
-----
Broadcast Message from <user>@<computer name>
(/dev/ttys001) at 21:30 CEST...
Executing automatic power-fail shutdown
———
and
———
sudo upsmon -D
Network UPS Tools upsmon 2.7.4
kill: No such process
0.000000 UPS: ups@<ip address> (slave) (power value 1)
0.000718 Using power down flag file /etc/killpower
0.001192 debug level is '1'
0.008274 Trying to connect to UPS [ups@<ip adddress>]
0.009866 Logged into UPS ups@<ip adddress>
290.089253 Critical UPS: ups@<ip adddress>
290.089313 Shutting down any UPSes in MASTER mode...
290.089322 Executing automatic power-fail shutdown
Broadcast Message from <user>@<computer name>
(/dev/ttys001) at 21:30 CEST...
Executing automatic power-fail shutdown
Kind regards,
Rob
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20170608/e4d1a86c/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: smime.p7s
Type: application/pkcs7-signature
Size: 3583 bytes
Desc: not available
URL: <http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20170608/e4d1a86c/attachment.bin>
More information about the Nut-upsuser
mailing list