[Nut-upsuser] debian 8 "jessie" nut 2.7.2 slaves not shutting down

Drew Plaster Drew.Plaster at otak.com
Thu Oct 19 15:05:04 UTC 2017


Roger,

The topology is:
	UPS TOPAPC, Data link to master, Power supply to master, slave1 and slave2
	UPS MIDAPC, Data link to master, Power supply to master, slave1 and slave2
	UPS BOTAPC, Data link to master, Power supply to master, slave1 and slave2

Shutdown plan:
When wall power fails for any of the three UPS units, they continue powering the master and the two slaves.  When two of the UPS battery have been depleted and the last (MINSUPPLIES 1) UPS unit reaches the status [OB LB]. the two slaves are shut down, and then the master is shutdown and sends shutdown signal to UPS (#POWERDOWNFLAG /etc/killpower) has been temporarily remarked out in the masters upsmon.conf to test if the slaves would shutdown vai hotsync or deadtime.
Anyway, that is how I was envisioning it functioning with the current config files; I may be mis-understanding something but that is the desired shutdown plan.

I don't know if this helps with anything but if I execute upsmon -c fsd on any of the three systems that system does shutdown but when I execute it on the master system it does not shutdown either of the slave systems.
 
Drew Plaster | Systems Administrator
808 SW 3rd Avenue, Suite 300 | Portland, OR 97204
o: 503.415.2385 | c: 503.484.0168 | f: 503.415.2498
www.otak.com
 
at Otak, we consider the environment before printing emails.
 
Disclaimer:
The information transmitted in this e-mail message and attachments, if any, may contain confidential material, and is intended only for the use of the individual or entity named above. Distribution to, or review by, unauthorized persons is prohibited. In the event of the unauthorized use of any material in this transmission, neither Otak nor the sender shall have any liability and the recipient shall defend, indemnify and hold harmless the sender, Otak and its principals, agents, employees and subconsultants from all related claims and damages. The recipient understands and agrees that any use or distribution of the material in this transmission is conditioned upon the acceptance of the terms stated in this disclaimer. If you have received this transmission in error, immediately notify the sender and permanently delete this transmission including attachments, if any.

-----Original Message-----
From: Nut-upsuser [mailto:nut-upsuser-bounces+drew.plaster=otak.com at lists.alioth.debian.org] On Behalf Of Roger Price
Sent: Thursday, October 19, 2017 2:49 AM
To: nut-upsuser Mailing List
Subject: Re: [Nut-upsuser] debian 8 "jessie" nut 2.7.2 slaves not shutting down

On Wed, 18 Oct 2017, Drew Plaster wrote:

> 	MASTER SYSTEM
>
> 	nut.conf
> MODE=netserver
>
> 	ups.conf
> [TOPAPC]
>     driver = usbhid-ups
>       port = auto
>      pollonly
>      serial = "IS1309002707"
>      desc = "TOPAPC"
> [MIDAPC]
>       driver = usbhid-ups
>         port = auto
>        pollonly
>        serial = "IS1309001233"
>        desc = "MIDAPC"
> [BOTAPC]
>       driver = usbhid-ups
>         port = auto
>        pollonly
>        serial = "IS1309001213"
>        desc = "BOTAPC"

Just to be sure that I understand your topology:

UPS TOPAPC, Data link to master, Power supply to master UPS MIDAPC, Data link to master, Power supply to slave1 UPS BOTAPC, Data link to master, Power supply to slave2

Shutdown plan:  When wall power fails for any one of the three UPS units, they continue powering the master and the two slaves.  When any one of the three UPS units reaches the status [OB LB]. the two slaves are shut down, and then the master is shutdown.

Is this correct? 
Roger