[Nut-upsuser] building on Solus
MTS
mts5204 at bigpond.com
Sun Sep 17 22:33:34 UTC 2017
Hi Charles,
I am using the same configs as I have in Linux Mint. What do I need to
change here?
ups.conf
[defender]
driver = blazer_usb
port = auto
pollinterval = 5
desc = "PowerShield Defender 650"
upsd
default.battery.voltage.high = 13.70
default.battery.voltage.low = 10.40
upsd.users
[local_mon]
password = ********
allowfrom = localhost
actions = set
actions = fsd
instcmds = all
upsmon master
upsmon.conf
MONITOR defender at localhost 1 local_mon *********** master
On 17/09/17 22:12, Charles Lepple wrote:
> On Sep 17, 2017, at 3:26 AM, MTS <mts5204 at bigpond.com> wrote:
>> 0.003814 Trying to connect to UPS [defender at localhost]
>> 0.004327 Login on UPS [defender at localhost] failed - got [ERR ACCESS-DENIED]
> The MONITOR line in upsmon.conf needs to match a NUT user in upsd.users.
>
> http://networkupstools.org/docs/man/upsmon.conf.html
>
> http://networkupstools.org/docs/man/upsd.users.html
>
> Looks like you are using this as a master system (UPS is directly connected, and upsmon shuts down that system), so the appropriate NUT user needs "upsmon master" in upsd.users.
>
> Note that the NUT users listed in upsd.users do not need to correspond to actual system users - think of them more as roles. If you add a slave system that connects over the network, you might not want it to be able to shut down the master, so you would use a different NUT username with "upsmon slave" privileges.