[Nut-upsuser] TrippLite SMX1500LCDT FreeBSD 11.2 trouble

Charles Lepple clepple at gmail.com
Thu Aug 23 13:51:12 BST 2018


On Aug 22, 2018, at 2:03 PM, Valentin Merkulov <schnobel at ickis.net> wrote:
> 
> With interruptonly the driver output goes into a loop (is it an
> expected behavior?)

Yes, this is what the driver does in the background if you do not pass any "-D" flags. If you were to start `upsd` at that point, it should be able to provide data to clients like `upsc`. However, since you needed to pass `-u root` to the driver, you may need to pass `-u root` to `upsd` as well.

> After I interrupt the loop and launch the driver
> again, it would return "No matching HID device found" until I unplug /
> re-plug USB cable.

I am not sure which component is at fault: NUT for not resetting something (though the automatic close-on-exit behavior in the OS should take care of this - or at least, it has in every other case I am aware of), libusb or FreeBSD for not cleaning up, or the UPS for not recovering properly.

Issue logged: https://github.com/networkupstools/nut/issues/600