[Nut-upsuser] Low battery unexpected shutdown

nicolae788 nicolae788 at gmail.com
Thu Apr 23 18:41:30 BST 2020


Hello. Battery, battery, battery. I am only thinking at worn batteries. I
recently had the same symptoms with an hp/eaton g3 1500va. One of the 3
batteries was reading a healthy 12.8v, but when put under load it would
quickly drain. I would measure each battery and test them under load, like
with a car headlight bulb switched on both fillaments.

On Thu, 23 Apr 2020, 16:54 Marc Franquesa, <marc.franquesa at gmail.com> wrote:

> Hi, recently I observed that during a power outage, my NUT setup doesn't
> shutdown properly. Indeed it never reaches the LowBattery state to notify
> and initiate shutdown on clients. Reviewing my setup and logs I think I'm
> facing multiple problems and I'm unable to point to real root cause.
>
> First, let me focus on my scenario and current setup:
>
> In normal status (ONLINE, fully charged) my UPS runtime is about
> 20minutes, this is some of the relevant info:
>
> Charge                    100%
> Charge Low                20%
> Runtime                   20m37s
> Type                      PbAc
> Manufacturer              EATON
> Model                     Ellipse
> ECO                       1200
> Serial                    000000000
> Power                     25VA
> Frequency Nominal         50Hz
> Voltage                   230.0V
> Voltage Nominal           230V
> Delay Shutdown            25s
> Delay Start               40s
> Firmware                  02
> Load                      23%
> Power Nominal             1200VA
> Status                    OL
>
> During a power outage it used to last for about 15 minutes and then
> initiate the shutdown. however reviewing the logs of my systems:
>
> Apr 19 12:04:23 - OnBattery
> Apr 19 12:10:21 - Power from UPS cut, all systems got suddenly powered off
> (no graceful shutdown)
> Apr 19 12:16:46 - Power restored, UPS feeds power again to the systems and
> they boot up.
>
> So this indicated the UPS only lasted about 6 minutes.
>
> Also I have 2 UPS:
> - UPSdevice, which is the real UPS
> - HeartBeat : virtual dummy device to monitor proper NUT communication
> (see http://rogerprice.org/NUT/NUT.html#HEARTBEAT).
>
> Looking at the logs when the event starts:
>
> Apr 19 12:04:23 laney upsmon[756]: UPS UPSdevice at power.srv.l3jane.net: On
> battery.
> Apr 19 12:04:23 laney upssched[797]: New timer: onbattwarn (30 seconds)
> Apr 19 12:04:53 laney upssched[797]: Event: onbattwarn
> Apr 19 12:08:24 laney upsmon[756]: UPS HeartBeat at power.srv.l3jane.net: On
> battery.
> Apr 19 12:08:24 laney upssched[797]: Cancelling timer: heartbeat-failure
>
> UPSdevice uses timer "onbattwarn", while HeartBeat is using a separated
> timer "heartbeat-failure". So I supose that when heartbeat cancels the
> 'heartbeat-failure' the onbattwarn timer is still running.
>
> The second concern is quickly spotted:
>
> Apr 19 12:09:19 laney usbhid-ups[703]: libusb_get_interrupt: error
> submitting URB: No such device
> Apr 19 12:09:24 laney upsd[753]: Data for UPS [UPSdevice] is stale - check
> driver
> Apr 19 12:09:26 laney upsd[753]: UPS [UPSdevice] data is no longer stale
>
> Seems that during the 'onbattwarn' event, NUT lost communcaiton with the
> UPS for about 6 secs? this is really quick to trigger any 'COMM_BAD' evebt
> so no notifcation regarding this is sent, just the logs.
>
> However as stated above on the logs, just 1 min later (12:10:21) power is
> totally lost even from UPS, no trace of LowBattery events, comm errors or
> so. A part from a email message that upssched sent me (although no logs of
> the event appears), this email reports:
>
> Power ups UPSdevice battery-low notification
> UPS:         UPSdevice at power.srv.l3jane.net
> Notice type: LOWBATT
> Message:     battery-low
> Sun, 19 Apr 2020 12:10:27 +0200
>
> Charge                    73%
> Charge Low                20%
> Runtime                   15m52s
> Type                      PbAc
> Manufacturer              EATON
> Model                     Ellipse
> ECO                       1200
> Serial                    000000000
> Type                      Ups
> Power                     25VA
> Frequency Nominal         50Hz
> Voltage                   230.0V
> Voltage Nominal           230V
> Delay Shutdown            20s
> Delay Start               30s
> Firmware                  02
> Load                      21%
> Power Nominal             1200VA
> Status                    FSD
> ALARM                     OB LB
>
> So, indeed was in LowBattery and FSD shutdown, however note that the
> current charge was 73% >> 20% low battery, so why it set LB when there were
> enough battery to run? Is this a comm problem, device issue, driver ?
>
> So mainly my concerns questions are:
> A) Can upsched introduce some race-conditions making a timer cancel cancel
> other timers not related ?
> B) May my UPS be faulting or just some USB driver issue?
>
> Any other hint, information or idea is welcomed.
>
> Regards
> _______________________________________________
> Nut-upsuser mailing list
> Nut-upsuser at alioth-lists.debian.net
> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://alioth-lists.debian.net/pipermail/nut-upsuser/attachments/20200423/af10d426/attachment-0001.html>


More information about the Nut-upsuser mailing list