[Nut-upsuser] unexpected UPS status

Roger Price roger at rogerprice.org
Wed Jan 8 11:44:03 GMT 2020


On Tue, 7 Jan 2020, Eyal Lebedinsky wrote:

> On 2020-01-07 23:01, Roger Price wrote:
>> There is no report for variable "ups.delay.start" in your upsc output.
>> What does command "upsc <ups> ups.delay.start" report?
> 
> $ upsc eaton ups.delay.start
> Init SSL without certificate database
> Error: Variable not supported by UPS

I am surprised that there is no ups.delay.start for this UPS.

> $ upsrw eaton
> [outlet.desc]
> [output.voltage.nominal]
> [ups.delay.shutdown]
> [ups.start.battery]

It looks as if this UPS unit is not capable of delaying a restart on wall power 
return until a given charge level has been reached.  This is the same situation 
as shown for the Eaton 5E 1100iUSB at 
https://networkupstools.org/ddl/Eaton/5E1100iUSB.html

Roger