[Nut-upsuser] Low Battery Problems
Gene Heskett
gheskett at shentel.net
Mon Jun 22 23:50:25 BST 2020
On Monday 22 June 2020 18:03:16 Charles Lepple wrote:
> On Jun 22, 2020, at 3:36 PM, Charles Lepple wrote:
> > On Jun 22, 2020, at 1:26 PM, Gene Heskett wrote:
> >> So I just edited /etc/nut/upsd.users to add both the commands it
> >> claims to have but get this response to either:
> >
> > In your original example, you had multiple “instcmd =“ lines for one
> > user- I think the allowed commands all need to be listed on one
> > instcmd line.
>
> Ignore this, I misremembered (and didn't read far enough down the URL
> I sent). Multiple allowed commands are specified with one command per
> instcmd.
Or as instcmds = ALL, which also doesn't work, ACCESS-DENIED.
Aha! Found it, very old version of upsmon.conf had gene as operayor, not
pi, but that didn't fix it until it had all been restarted, so a quick
battery test is underway. And it was quick, 15 secs OB.
So a .deep its running now.
Broadcast message from nut at rpi4.coyote.den (somewhere) (Mon Jun 22
18:35:49 202
UPS myups at localhost on battery
upsc myups says zero load, battery.runtime: 4080
The pi don't draw a lot when its not busy.
I assume it will use about 90 % & switch back to line ending the a deep
test?
In which case this might take hours,
Cheers, Gene Heskett
--
"There are four boxes to be used in defense of liberty:
soap, ballot, jury, and ammo. Please use in that order."
-Ed Howdershelt (Author)
If we desire respect for the law, we must first make the law respectable.
- Louis D. Brandeis
Genes Web page <http://geneslinuxbox.net:6309/gene>
More information about the Nut-upsuser
mailing list