[Nut-upsuser] ups.test.result meaning
Rick Dicaire
kritek at gmail.com
Sun Nov 1 00:13:48 GMT 2020
On Sat, Oct 31, 2020 at 2:42 PM Tim Dawson <tadawson at tpcsvc.com> wrote:
> I'm going to guess that since your test runtime of 305 is very close to
> the low limit of 300, that's the warning. Not yet a fail, but very, very
> close.
>
I tried setting
override.battery.runtime.low = 60
in ups.conf, and waited for the UPS to reach 100% charge, and ups.status to
report only OL.
I initiated another test.battery.start.quick.
Same kind of result:
battery.charge: 31
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 255
battery.runtime.low: 60
battery.type: PbAcid
battery.voltage: 16.0
battery.voltage.nominal: 24
device.mfr: CP1350PFCLCD
device.model: CRCA102\#BJ1
device.serial: CPS
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 5
driver.parameter.port: auto
driver.parameter.vendorid: 0764
driver.version: 2.7.2
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.38
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 122.0
input.voltage.nominal: 120
output.voltage: 138.0
ups.beeper.status: disabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 36
ups.mfr: CP1350PFCLCD
ups.model: CRCA102#BJ1
ups.productid: 0501
ups.realpower.nominal: 810
ups.serial: CPS
ups.status: OL CHRG LB
ups.test.result: Done and warning
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764
I'm trying to determine if I need to replace the batteries/device, its out
of warranty at this rate anyway.
Any more ideas?