[Nut-upsuser] ups.test.result meaning
Rick Dicaire
kritek at gmail.com
Sun Nov 1 01:59:32 GMT 2020
>
>
> > battery.voltage: 16.0
> At that voltage, 5 of the 12 cells are shorted
> > output.voltage: 138.0
> too high by about 15 volts
>
> Wow! That battery is beyond toasted, shoulda been replaced months ago.
> And the output voltage is a bit much if its truthfull.
>
Thanks for the response Gene!
I've ordered a replacement unit.
I'm not sure about the output voltage readings, I have four CyberPower
CP1500AVRLCDa UPSs and they all show 136-139v output.
My CyberPower OR1500LCDMRM1U reports 124v.
I still don't know what triggers the warning in the test though...