[Nut-upsuser] Can't get CyberPower UPS to work with Raspberry Pi 4
Gene Heskett
gheskett at shentel.net
Mon Oct 26 13:38:22 GMT 2020
On Monday 26 October 2020 09:01:31 Charles Lepple wrote:
> On Oct 25, 2020, at 11:52 AM, Robert Stocker <kneadtoknow at gmail.com>
wrote:
> > Init SSL without certificate database
> > battery.charge: 100
> > battery.charge.low: 10
> > battery.charge.warning: 20
> > battery.mfr.date: CPS
> > battery.runtime: 15690
> > battery.runtime.low: 300
> > battery.type: PbAcid
> > battery.voltage: 24.0
> > battery.voltage.nominal: 24
>
> I don't have the citation handy, but I think another user reported
> that the battery.voltage returned by the UPS is a constant 24.0 V,
> regardless of the actual battery voltage.
>
> > device.mfr: CPS
> > device.model: CST135XLU
> > device.serial: CR7EO2003120
> > device.type: ups
> > driver.name: usbhid-ups
> > driver.parameter.pollfreq: 30
> > driver.parameter.pollinterval: 5
> > driver.parameter.port: auto
> > driver.parameter.synchronous: no
> > driver.version: 2.7.4
> > driver.version.data: CyberPower HID 0.4
> > driver.version.internal: 0.41
> > input.voltage: 121.0
> > input.voltage.nominal: 120
> > output.voltage: 137.0
>
> Given the description on the product page you sent earlier, the UPS is
> likely not providing 137.0 V, but is bypassing the transformer since
> the power is good.
>
> https://www.cyberpowersystems.com/product/ups/battery-backup/cst135xlu
>/
>
> This is another known CyberPower issue, and fixing it properly
> requires making some changes deep in the core USB HID code (that would
> require a lot of testing on other vendors' equipment) for what is
> basically a cosmetic issue:
>
> https://github.com/networkupstools/nut/issues/439
>
> > ups.beeper.status: disabled
> > ups.delay.shutdown: 20
> > ups.delay.start: 30
>
> For these delays, note there seems to be an issue with
> ondelay/ups.delay.start:
>
> https://github.com/networkupstools/nut/issues/625
>
> and rounding of the timers down to the next lower minute:
>
> https://github.com/networkupstools/nut/blob/f3a40e4595c1f18368f89b9af3
>38bfe52dd06846/docs/man/usbhid-ups.txt#L53-L78
>
> so basically I'd recommend testing shutdown extensively.
>
> > ups.load: 4
> > ups.mfr: CPS
> > ups.model: CST135XLU
> > ups.productid: 0501
> > ups.realpower.nominal: 810
> > ups.serial: CR7EO2003120
> > ups.status: OL
> > ups.test.result: No test initiated
> > ups.timer.shutdown: -60
> > ups.timer.start: -60
> > ups.vendorid: 0764
> >
> > If you run systemctl, you should see something like this:
> >
> > And here's what I got from that:
> >
> > nut-driver.service loaded active running Network UPS Tools
> > - power device driver controller nut-monitor.service loaded
> > active running Network UPS Tools - power device monitor and
> > shutdown controller nut-server.service loaded active running
> > Network UPS Tools - power devices information server
>
I think it may be dependent on thhe ups. I have a 625 WA cyberpower on an
rpi4, and I believe its more truthfull. Is this helpfull?
pi at rpi4:/media/pi/workspace $ upsc myups
Init SSL without certificate database
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 4410
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 14.5
battery.voltage.nominal: 12
device.mfr: CPS
device.model: CP625HGa
device.type: ups
driver.name: usbhid-ups
driver.parameter.offdelay: 120
driver.parameter.ondelay: 0
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.synchronous: no
driver.version: 2.7.4
driver.version.data: CyberPower HID 0.4
driver.version.internal: 0.41
input.transfer.high: 0
input.transfer.low: 0
input.voltage: 124.0
input.voltage.nominal: 120
output.voltage: 124.0
ups.beeper.status: enabled
ups.delay.shutdown: 120
ups.delay.start: 0
ups.load: 8
ups.mfr: CPS
ups.model: CP625HGa
ups.productid: 0501
ups.realpower.nominal: 375
ups.status: OL
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: 0
ups.vendorid: 0764
It has to hold up the pi, but only long enough for the 20kw nat gas fired
generac outside the back garage door to start, nominally 5 seconds
according to its -wall broadcasts. It shuts down if unplugged in only a
couple minutes, but will not accept a longer timeout. It does do the job
I bought it to do. The pi's draw and the interface card is about 13 or
14 WA.
> _______________________________________________
> Nut-upsuser mailing list
> Nut-upsuser at alioth-lists.debian.net
> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
Cheers, Gene Heskett
--
"There are four boxes to be used in defense of liberty:
soap, ballot, jury, and ammo. Please use in that order."
-Ed Howdershelt (Author)
If we desire respect for the law, we must first make the law respectable.
- Louis D. Brandeis
Genes Web page <http://geneslinuxbox.net:6309/gene>
More information about the Nut-upsuser
mailing list