[Nut-upsuser] No Shutdown Signal being Sent
Roger Price
roger at rogerprice.org
Mon Aug 16 22:40:23 BST 2021
On Mon, 16 Aug 2021, bobby via Nut-upsuser wrote:
> I setup my raspberry pi to monitor my CyberPower 1500VA. I tested NUT by
> unplugging the UPS. Upon unplugging the UPS from the outlet, the upsmon shows
> that the UPS is on battery, then it is back on line power, once as I plug the
> UPS back in. But the server is never sent the shutdown signal. How do I get
> it so that the server is sent the shutdown signal?
What you are seeing is the correct behaviour. upsmon will not shut down your
system until the battery charge drops below the value given by command
upsc <ups> battery.charge.low
If you want a faster shutdown, either raise the value of battery.charge.low or
use timers.
Roger
More information about the Nut-upsuser
mailing list