[Nut-upsuser] nut-monitor service fails even though nut-monitor seems to work
Nathan Dehnel
ncdehnel at gmail.com
Mon Aug 30 01:02:14 BST 2021
The systemd service fails even though the output seems to indicate
that nut-monitor is communicating successfully with the UPS.
Gentoo Linux
Nut v2.7.4-r7 (installed from distro package)
UPS: Tripplite SU1500RTXLCD2U (controlled by pfsense)
journalctl output:
-- Boot 93e0d5b24bac491994a2ea5cce08cdcc --
Aug 16 23:45:40 gentoodesktop systemd[1]: Starting Network UPS Tools -
power device monitor and shutdown controller...
░░ Subject: A start job for unit nut-monitor.service has begun execution
░░ Defined-By: systemd
░░ Support: https://gentoo.org/support/
░░
░░ A start job for unit nut-monitor.service has begun execution.
░░
░░ The job identifier is 107.
Aug 16 23:45:40 gentoodesktop upsmon[1943]: kill: No such process
Aug 16 23:45:40 gentoodesktop upsmon[1943]: 0.000000 UPS:
tripplite1 at pfsense (slave) (power value 1)
Aug 16 23:45:40 gentoodesktop upsmon[1943]: 0.000019 UPS:
heartbeat at localhost (monitoring only)
Aug 16 23:45:40 gentoodesktop upsmon[1943]: 0.000051 Using
power down flag file /etc/killpower
Aug 16 23:45:40 gentoodesktop upsmon[1943]: 0.000127 debug
level is '8'
Aug 16 23:45:40 gentoodesktop upsmon[1944]: 0.003931 Trying
to connect to UPS [tripplite1 at pfsense]
Aug 16 23:45:52 gentoodesktop upsmon[1944]: 12.452582 UPS
[tripplite1 at pfsense]: connect failed: No such host
Aug 16 23:45:52 gentoodesktop upsmon[1944]: 12.452600
do_notify: ntype 0x0005 (COMMBAD)
Aug 16 23:45:52 gentoodesktop upsmon[1944]: 12.452725 Trying
to connect to UPS [heartbeat at localhost]
Aug 16 23:45:52 gentoodesktop upsmon[1944]: 12.453032 Can not
connect to localhost in SSL, continue uncrypted
Aug 16 23:45:52 gentoodesktop upsmon[1944]: 12.457065 Logged
into UPS heartbeat at localhost
Aug 16 23:45:52 gentoodesktop upsmon[1944]: 12.457104
pollups: heartbeat at localhost
Aug 16 23:45:52 gentoodesktop upsmon[1944]: 12.457110
get_var: heartbeat at localhost / status
Aug 16 23:45:52 gentoodesktop upsmon[1944]: 12.457142
parse_status: [OL]
Aug 16 23:45:52 gentoodesktop upsmon[1944]: 12.457148 parsing: [OL]
Aug 16 23:45:52 gentoodesktop upsmon[1944]: 12.457151
ups_on_line: heartbeat at localhost (first time)
Aug 16 23:45:52 gentoodesktop upsmon[1944]: 12.457154 Current
power value: 1
Aug 16 23:45:52 gentoodesktop upsmon[1944]: 12.457157 Minimum
power value: 1
Aug 16 23:45:57 gentoodesktop upsmon[1944]: 17.457224 Trying
to connect to UPS [tripplite1 at pfsense]
Aug 16 23:45:57 gentoodesktop upsmon[1944]: 17.457992 Can not
connect to pfsense in SSL, continue uncrypted
Aug 16 23:45:57 gentoodesktop upsmon[1944]: 17.458515 Logged
into UPS tripplite1 at pfsense
Aug 16 23:45:57 gentoodesktop upsmon[1944]: 17.458525
pollups: tripplite1 at pfsense
Aug 16 23:45:57 gentoodesktop upsmon[1944]: 17.458529
get_var: tripplite1 at pfsense / status
Aug 16 23:45:57 gentoodesktop upsmon[1944]: 17.458629
parse_status: [OL]
Aug 16 23:45:57 gentoodesktop upsmon[1944]: 17.458637
do_notify: ntype 0x0004 (COMMOK)
Aug 16 23:45:57 gentoodesktop upsmon[1944]: 17.458640
Communications with UPS tripplite1 at pfsense established
Aug 16 23:45:57 gentoodesktop upsmon[1944]: 17.458811 parsing: [OL]
Aug 16 23:45:57 gentoodesktop upsmon[1944]: 17.458822
ups_on_line: tripplite1 at pfsense (first time)
Aug 16 23:45:57 gentoodesktop upsmon[1944]: 17.458824
pollups: heartbeat at localhost
Aug 16 23:45:57 gentoodesktop upsmon[1944]: 17.458826
get_var: heartbeat at localhost / status
Aug 16 23:45:57 gentoodesktop upsmon[1944]: 17.458880
parse_status: [OL]
Aug 16 23:45:57 gentoodesktop upsmon[1944]: 17.458887 parsing: [OL]
Aug 16 23:45:57 gentoodesktop upsmon[1944]: 17.458890
ups_on_line: heartbeat at localhost (no change)
Aug 16 23:45:57 gentoodesktop upsmon[1944]: 17.458892 Current
power value: 1
Aug 16 23:45:57 gentoodesktop upsmon[1944]: 17.458894 Minimum
power value: 1
Aug 16 23:45:57 gentoodesktop upsmon[2076]: wall: /dev/pts/0: No such
file or directory
Aug 16 23:45:57 gentoodesktop upsmon[2076]: wall: /dev/pts/1: No such
file or directory
Aug 16 23:45:57 gentoodesktop upsmon[2076]: wall: /dev/pts/11: No such
file or directory
Aug 16 23:45:57 gentoodesktop upsmon[2076]: wall: /dev/pts/8: No such
file or directory
Aug 16 23:45:57 gentoodesktop upsmon[2076]: wall: /dev/pts/4: No such
file or directory
Aug 16 23:45:57 gentoodesktop upsmon[2076]: wall: /dev/pts/9: No such
file or directory
Aug 16 23:45:57 gentoodesktop upsmon[2075]: Network UPS Tools upsmon 2.7.4
Aug 16 23:46:00 gentoodesktop upsmon[1947]: Failed to connect to
parent and failed to create parent: No such file or directory
Aug 16 23:46:00 gentoodesktop upssched[1947]: Failed to connect to
parent and failed to create parent: No such file or directory
Aug 16 23:46:00 gentoodesktop upsmon[1946]: Network UPS Tools upsmon 2.7.4
Aug 16 23:46:04 gentoodesktop upsmon[1944]: 22.458958
pollups: tripplite1 at pfsense
Aug 16 23:46:04 gentoodesktop upsmon[1944]: 22.458973
get_var: tripplite1 at pfsense / status
Aug 16 23:46:04 gentoodesktop upsmon[1944]: 22.459248
parse_status: [OL]
Aug 16 23:46:04 gentoodesktop upsmon[1944]: 22.459251 parsing: [OL]
Aug 16 23:46:04 gentoodesktop upsmon[1944]: 22.459253
ups_on_line: tripplite1 at pfsense (no change)
Aug 16 23:46:04 gentoodesktop upsmon[1944]: 22.459255
pollups: heartbeat at localhost
Aug 16 23:46:04 gentoodesktop upsmon[1944]: 22.459257
get_var: heartbeat at localhost / status
Aug 16 23:46:04 gentoodesktop upsmon[1944]: 22.459293
parse_status: [OL]
Aug 16 23:46:04 gentoodesktop upsmon[1944]: 22.459296 parsing: [OL]
Aug 16 23:46:04 gentoodesktop upsmon[1944]: 22.459299
ups_on_line: heartbeat at localhost (no change)
Aug 16 23:46:04 gentoodesktop upsmon[1944]: 22.459301 Current
power value: 1
Aug 16 23:46:04 gentoodesktop upsmon[1944]: 22.459304 Minimum
power value: 1
Aug 16 23:46:07 gentoodesktop upsmon[1944]: 27.459380
pollups: tripplite1 at pfsense
Aug 16 23:46:07 gentoodesktop upsmon[1944]: 27.459394
get_var: tripplite1 at pfsense / status
Aug 16 23:46:07 gentoodesktop upsmon[1944]: 27.459677
parse_status: [OL]
Aug 16 23:46:07 gentoodesktop upsmon[1944]: 27.459681 parsing: [OL]
Aug 16 23:46:07 gentoodesktop upsmon[1944]: 27.459682
ups_on_line: tripplite1 at pfsense (no change)
Aug 16 23:46:07 gentoodesktop upsmon[1944]: 27.459684
pollups: heartbeat at localhost
Aug 16 23:46:07 gentoodesktop upsmon[1944]: 27.459686
get_var: heartbeat at localhost / status
Aug 16 23:46:07 gentoodesktop upsmon[1944]: 27.459722
parse_status: [OL]
Aug 16 23:46:07 gentoodesktop upsmon[1944]: 27.459725 parsing: [OL]
Aug 16 23:46:07 gentoodesktop upsmon[1944]: 27.459727
ups_on_line: heartbeat at localhost (no change)
Aug 16 23:46:07 gentoodesktop upsmon[1944]: 27.459729 Current
power value: 1
Aug 16 23:46:07 gentoodesktop upsmon[1944]: 27.459731 Minimum
power value: 1
Aug 16 23:46:12 gentoodesktop upsmon[1944]: 32.459807
pollups: tripplite1 at pfsense
Aug 16 23:46:12 gentoodesktop upsmon[1944]: 32.459822
get_var: tripplite1 at pfsense / status
Aug 16 23:46:12 gentoodesktop upsmon[1944]: 32.460038
parse_status: [OL]
Aug 16 23:46:12 gentoodesktop upsmon[1944]: 32.460041 parsing: [OL]
Aug 16 23:46:12 gentoodesktop upsmon[1944]: 32.460043
ups_on_line: tripplite1 at pfsense (no change)
Aug 16 23:46:12 gentoodesktop upsmon[1944]: 32.460044
pollups: heartbeat at localhost
Aug 16 23:46:12 gentoodesktop upsmon[1944]: 32.460046
get_var: heartbeat at localhost / status
Aug 16 23:46:12 gentoodesktop upsmon[1944]: 32.460086
parse_status: [OL]
Aug 16 23:46:12 gentoodesktop upsmon[1944]: 32.460088 parsing: [OL]
Aug 16 23:46:12 gentoodesktop upsmon[1944]: 32.460089
ups_on_line: heartbeat at localhost (no change)
Aug 16 23:46:12 gentoodesktop upsmon[1944]: 32.460091 Current
power value: 1
Aug 16 23:46:12 gentoodesktop upsmon[1944]: 32.460093 Minimum
power value: 1
Aug 16 23:46:19 gentoodesktop upsmon[1944]: 39.140972
pollups: tripplite1 at pfsense
Aug 16 23:46:19 gentoodesktop upsmon[1944]: 39.140986
get_var: tripplite1 at pfsense / status
Aug 16 23:46:19 gentoodesktop upsmon[1944]: 39.141227
parse_status: [OL]
Aug 16 23:46:19 gentoodesktop upsmon[1944]: 39.141230 parsing: [OL]
Aug 16 23:46:19 gentoodesktop upsmon[1944]: 39.141232
ups_on_line: tripplite1 at pfsense (no change)
Aug 16 23:46:19 gentoodesktop upsmon[1944]: 39.141234
pollups: heartbeat at localhost
Aug 16 23:46:19 gentoodesktop upsmon[1944]: 39.141236
get_var: heartbeat at localhost / status
Aug 16 23:46:19 gentoodesktop upsmon[1944]: 39.141286
parse_status: [OL]
Aug 16 23:46:19 gentoodesktop upsmon[1944]: 39.141288 parsing: [OL]
Aug 16 23:46:19 gentoodesktop upsmon[1944]: 39.141290
ups_on_line: heartbeat at localhost (no change)
Aug 16 23:46:19 gentoodesktop upsmon[1944]: 39.141292 Current
power value: 1
Aug 16 23:46:19 gentoodesktop upsmon[1944]: 39.141294 Minimum
power value: 1
Aug 16 23:46:24 gentoodesktop upsmon[1944]: 44.141355
pollups: tripplite1 at pfsense
Aug 16 23:46:24 gentoodesktop upsmon[1944]: 44.141371
get_var: tripplite1 at pfsense / status
Aug 16 23:46:24 gentoodesktop upsmon[1944]: 44.141610
parse_status: [OL]
Aug 16 23:46:24 gentoodesktop upsmon[1944]: 44.141613 parsing: [OL]
Aug 16 23:46:24 gentoodesktop upsmon[1944]: 44.141615
ups_on_line: tripplite1 at pfsense (no change)
Aug 16 23:46:24 gentoodesktop upsmon[1944]: 44.141617
pollups: heartbeat at localhost
Aug 16 23:46:24 gentoodesktop upsmon[1944]: 44.141618
get_var: heartbeat at localhost / status
Aug 16 23:46:24 gentoodesktop upsmon[1944]: 44.141652
parse_status: [OL]
Aug 16 23:46:24 gentoodesktop upsmon[1944]: 44.141654 parsing: [OL]
Aug 16 23:46:24 gentoodesktop upsmon[1944]: 44.141656
ups_on_line: heartbeat at localhost (no change)
Aug 16 23:46:24 gentoodesktop upsmon[1944]: 44.141658 Current
power value: 1
Aug 16 23:46:24 gentoodesktop upsmon[1944]: 44.141659 Minimum
power value: 1
Aug 16 23:46:29 gentoodesktop upsmon[1944]: 49.141723
pollups: tripplite1 at pfsense
Aug 16 23:46:29 gentoodesktop upsmon[1944]: 49.141737
get_var: tripplite1 at pfsense / status
Aug 16 23:46:29 gentoodesktop upsmon[1944]: 49.141981
parse_status: [OL]
Aug 16 23:46:29 gentoodesktop upsmon[1944]: 49.141985 parsing: [OL]
Aug 16 23:46:29 gentoodesktop upsmon[1944]: 49.141987
ups_on_line: tripplite1 at pfsense (no change)
Aug 16 23:46:29 gentoodesktop upsmon[1944]: 49.141989
pollups: heartbeat at localhost
Aug 16 23:46:29 gentoodesktop upsmon[1944]: 49.141990
get_var: heartbeat at localhost / status
Aug 16 23:46:29 gentoodesktop upsmon[1944]: 49.142026
parse_status: [OL]
Aug 16 23:46:29 gentoodesktop upsmon[1944]: 49.142028 parsing: [OL]
Aug 16 23:46:29 gentoodesktop upsmon[1944]: 49.142030
ups_on_line: heartbeat at localhost (no change)
Aug 16 23:46:29 gentoodesktop upsmon[1944]: 49.142032 Current
power value: 1
Aug 16 23:46:29 gentoodesktop upsmon[1944]: 49.142034 Minimum
power value: 1
Aug 16 23:46:34 gentoodesktop upsmon[1944]: 54.142098
pollups: tripplite1 at pfsense
Aug 16 23:46:34 gentoodesktop upsmon[1944]: 54.142116
get_var: tripplite1 at pfsense / status
Aug 16 23:46:34 gentoodesktop upsmon[1944]: 54.142405
parse_status: [OL]
Aug 16 23:46:34 gentoodesktop upsmon[1944]: 54.142411 parsing: [OL]
Aug 16 23:46:34 gentoodesktop upsmon[1944]: 54.142415
ups_on_line: tripplite1 at pfsense (no change)
Aug 16 23:46:34 gentoodesktop upsmon[1944]: 54.142418
pollups: heartbeat at localhost
Aug 16 23:46:34 gentoodesktop upsmon[1944]: 54.142420
get_var: heartbeat at localhost / status
Aug 16 23:46:34 gentoodesktop upsmon[1944]: 54.142463
parse_status: [OL]
Aug 16 23:46:34 gentoodesktop upsmon[1944]: 54.142466 parsing: [OL]
Aug 16 23:46:34 gentoodesktop upsmon[1944]: 54.142468
ups_on_line: heartbeat at localhost (no change)
Aug 16 23:46:34 gentoodesktop upsmon[1944]: 54.142471 Current
power value: 1
Aug 16 23:46:34 gentoodesktop upsmon[1944]: 54.142473 Minimum
power value: 1
Aug 16 23:46:39 gentoodesktop upsmon[1944]: 59.142539
pollups: tripplite1 at pfsense
Aug 16 23:46:39 gentoodesktop upsmon[1944]: 59.142560
get_var: tripplite1 at pfsense / status
Aug 16 23:46:39 gentoodesktop upsmon[1944]: 59.142807
parse_status: [OL]
Aug 16 23:46:39 gentoodesktop upsmon[1944]: 59.142810 parsing: [OL]
Aug 16 23:46:39 gentoodesktop upsmon[1944]: 59.142812
ups_on_line: tripplite1 at pfsense (no change)
Aug 16 23:46:39 gentoodesktop upsmon[1944]: 59.142815
pollups: heartbeat at localhost
Aug 16 23:46:39 gentoodesktop upsmon[1944]: 59.142817
get_var: heartbeat at localhost / status
Aug 16 23:46:39 gentoodesktop upsmon[1944]: 59.142859
parse_status: [OL]
Aug 16 23:46:39 gentoodesktop upsmon[1944]: 59.142862 parsing: [OL]
Aug 16 23:46:39 gentoodesktop upsmon[1944]: 59.142865
ups_on_line: heartbeat at localhost (no change)
Aug 16 23:46:39 gentoodesktop upsmon[1944]: 59.142867 Current
power value: 1
Aug 16 23:46:39 gentoodesktop upsmon[1944]: 59.142869 Minimum
power value: 1
Aug 16 23:46:44 gentoodesktop upsmon[1944]: 64.142936
pollups: tripplite1 at pfsense
Aug 16 23:46:44 gentoodesktop upsmon[1944]: 64.142961
get_var: tripplite1 at pfsense / status
Aug 16 23:46:44 gentoodesktop upsmon[1944]: 64.143253
parse_status: [OL]
Aug 16 23:46:44 gentoodesktop upsmon[1944]: 64.143263 parsing: [OL]
Aug 16 23:46:44 gentoodesktop upsmon[1944]: 64.143267
ups_on_line: tripplite1 at pfsense (no change)
Aug 16 23:46:44 gentoodesktop upsmon[1944]: 64.143271
pollups: heartbeat at localhost
Aug 16 23:46:44 gentoodesktop upsmon[1944]: 64.143275
get_var: heartbeat at localhost / status
Aug 16 23:46:44 gentoodesktop upsmon[1944]: 64.143339
parse_status: [OL]
Aug 16 23:46:44 gentoodesktop upsmon[1944]: 64.143343 parsing: [OL]
Aug 16 23:46:44 gentoodesktop upsmon[1944]: 64.143346
ups_on_line: heartbeat at localhost (no change)
Aug 16 23:46:44 gentoodesktop upsmon[1944]: 64.143349 Current
power value: 1
Aug 16 23:46:44 gentoodesktop upsmon[1944]: 64.143353 Minimum
power value: 1
Aug 16 23:46:51 gentoodesktop upsmon[1944]: 69.143418
pollups: tripplite1 at pfsense
Aug 16 23:46:51 gentoodesktop upsmon[1944]: 69.143432
get_var: tripplite1 at pfsense / status
Aug 16 23:46:51 gentoodesktop upsmon[1944]: 69.143670
parse_status: [OL]
Aug 16 23:46:51 gentoodesktop upsmon[1944]: 69.143673 parsing: [OL]
Aug 16 23:46:51 gentoodesktop upsmon[1944]: 69.143676
ups_on_line: tripplite1 at pfsense (no change)
Aug 16 23:46:51 gentoodesktop upsmon[1944]: 69.143678
pollups: heartbeat at localhost
Aug 16 23:46:51 gentoodesktop upsmon[1944]: 69.143680
get_var: heartbeat at localhost / status
Aug 16 23:46:51 gentoodesktop upsmon[1944]: 69.143721
parse_status: [OL]
Aug 16 23:46:51 gentoodesktop upsmon[1944]: 69.143724 parsing: [OL]
Aug 16 23:46:51 gentoodesktop upsmon[1944]: 69.143727
ups_on_line: heartbeat at localhost (no change)
Aug 16 23:46:51 gentoodesktop upsmon[1944]: 69.143730 Current
power value: 1
Aug 16 23:46:51 gentoodesktop upsmon[1944]: 69.143732 Minimum
power value: 1
Aug 16 23:46:54 gentoodesktop upsmon[1944]: 74.143797
pollups: tripplite1 at pfsense
Aug 16 23:46:54 gentoodesktop upsmon[1944]: 74.143818
get_var: tripplite1 at pfsense / status
Aug 16 23:46:54 gentoodesktop upsmon[1944]: 74.144094
parse_status: [OL]
Aug 16 23:46:54 gentoodesktop upsmon[1944]: 74.144097 parsing: [OL]
Aug 16 23:46:54 gentoodesktop upsmon[1944]: 74.144099
ups_on_line: tripplite1 at pfsense (no change)
Aug 16 23:46:54 gentoodesktop upsmon[1944]: 74.144100
pollups: heartbeat at localhost
Aug 16 23:46:54 gentoodesktop upsmon[1944]: 74.144103
get_var: heartbeat at localhost / status
Aug 16 23:46:54 gentoodesktop upsmon[1944]: 74.144143
parse_status: [OL]
Aug 16 23:46:54 gentoodesktop upsmon[1944]: 74.144147 parsing: [OL]
Aug 16 23:46:54 gentoodesktop upsmon[1944]: 74.144150
ups_on_line: heartbeat at localhost (no change)
Aug 16 23:46:54 gentoodesktop upsmon[1944]: 74.144153 Current
power value: 1
Aug 16 23:46:54 gentoodesktop upsmon[1944]: 74.144155 Minimum
power value: 1
Aug 16 23:46:59 gentoodesktop upsmon[1944]: 79.144221
pollups: tripplite1 at pfsense
Aug 16 23:46:59 gentoodesktop upsmon[1944]: 79.144249
get_var: tripplite1 at pfsense / status
Aug 16 23:46:59 gentoodesktop upsmon[1944]: 79.144484
parse_status: [OL]
Aug 16 23:46:59 gentoodesktop upsmon[1944]: 79.144489 parsing: [OL]
Aug 16 23:46:59 gentoodesktop upsmon[1944]: 79.144491
ups_on_line: tripplite1 at pfsense (no change)
Aug 16 23:46:59 gentoodesktop upsmon[1944]: 79.144494
pollups: heartbeat at localhost
Aug 16 23:46:59 gentoodesktop upsmon[1944]: 79.144497
get_var: heartbeat at localhost / status
Aug 16 23:46:59 gentoodesktop upsmon[1944]: 79.144554
parse_status: [OL]
Aug 16 23:46:59 gentoodesktop upsmon[1944]: 79.144558 parsing: [OL]
Aug 16 23:46:59 gentoodesktop upsmon[1944]: 79.144560
ups_on_line: heartbeat at localhost (no change)
Aug 16 23:46:59 gentoodesktop upsmon[1944]: 79.144563 Current
power value: 1
Aug 16 23:46:59 gentoodesktop upsmon[1944]: 79.144566 Minimum
power value: 1
Aug 16 23:47:04 gentoodesktop upsmon[1944]: 84.144636
pollups: tripplite1 at pfsense
Aug 16 23:47:04 gentoodesktop upsmon[1944]: 84.144664
get_var: tripplite1 at pfsense / status
Aug 16 23:47:04 gentoodesktop upsmon[1944]: 84.144934
parse_status: [OL]
Aug 16 23:47:04 gentoodesktop upsmon[1944]: 84.144942 parsing: [OL]
Aug 16 23:47:04 gentoodesktop upsmon[1944]: 84.144945
ups_on_line: tripplite1 at pfsense (no change)
Aug 16 23:47:04 gentoodesktop upsmon[1944]: 84.144947
pollups: heartbeat at localhost
Aug 16 23:47:04 gentoodesktop upsmon[1944]: 84.144950
get_var: heartbeat at localhost / status
Aug 16 23:47:04 gentoodesktop upsmon[1944]: 84.145008
parse_status: [OL]
Aug 16 23:47:04 gentoodesktop upsmon[1944]: 84.145013 parsing: [OL]
Aug 16 23:47:04 gentoodesktop upsmon[1944]: 84.145015
ups_on_line: heartbeat at localhost (no change)
Aug 16 23:47:04 gentoodesktop upsmon[1944]: 84.145018 Current
power value: 1
Aug 16 23:47:04 gentoodesktop upsmon[1944]: 84.145021 Minimum
power value: 1
Aug 16 23:47:09 gentoodesktop upsmon[1944]: 89.145087
pollups: tripplite1 at pfsense
Aug 16 23:47:09 gentoodesktop upsmon[1944]: 89.145107
get_var: tripplite1 at pfsense / status
Aug 16 23:47:09 gentoodesktop upsmon[1944]: 89.145389
parse_status: [OL]
Aug 16 23:47:09 gentoodesktop upsmon[1944]: 89.145394 parsing: [OL]
Aug 16 23:47:09 gentoodesktop upsmon[1944]: 89.145397
ups_on_line: tripplite1 at pfsense (no change)
Aug 16 23:47:09 gentoodesktop upsmon[1944]: 89.145399
pollups: heartbeat at localhost
Aug 16 23:47:09 gentoodesktop upsmon[1944]: 89.145404
get_var: heartbeat at localhost / status
Aug 16 23:47:09 gentoodesktop upsmon[1944]: 89.145450
parse_status: [OL]
Aug 16 23:47:09 gentoodesktop upsmon[1944]: 89.145453 parsing: [OL]
Aug 16 23:47:09 gentoodesktop upsmon[1944]: 89.145455
ups_on_line: heartbeat at localhost (no change)
Aug 16 23:47:09 gentoodesktop upsmon[1944]: 89.145458 Current
power value: 1
Aug 16 23:47:09 gentoodesktop upsmon[1944]: 89.145460 Minimum
power value: 1
Aug 16 23:47:12 gentoodesktop systemd[1]: nut-monitor.service: start
operation timed out. Terminating.
Aug 16 23:47:12 gentoodesktop upsmon[1944]: 91.852466 Signal
15: exiting
Aug 16 23:47:12 gentoodesktop upsmon[1944]: 91.852486
Dropping connection to UPS [tripplite1 at pfsense]
Aug 16 23:47:12 gentoodesktop upsmon[1944]: 91.852556
Dropping connection to UPS [heartbeat at localhost]
Aug 16 23:47:12 gentoodesktop upsmon[1944]: Network UPS Tools upsmon 2.7.4
Aug 16 23:47:12 gentoodesktop systemd[1]: nut-monitor.service: Failed
with result 'timeout'.
░░ Subject: Unit failed
░░ Defined-By: systemd
░░ Support: https://gentoo.org/support/
░░
░░ The unit nut-monitor.service has entered the 'failed' state with
result 'timeout'.
Aug 16 23:47:12 gentoodesktop systemd[1]: Failed to start Network UPS
Tools - power device monitor and shutdown controller.
░░ Subject: A start job for unit nut-monitor.service has failed
░░ Defined-By: systemd
░░ Support: https://gentoo.org/support/
░░
░░ A start job for unit nut-monitor.service has finished with a failure.
░░
░░ The job identifier is 107 and the job result is failed.
Aug 16 23:47:12 gentoodesktop systemd[1]: nut-monitor.service:
Triggering OnFailure= dependencies.
Aug 16 23:47:12 gentoodesktop systemd[1]: nut-monitor.service:
Consumed 2.054s CPU time.
░░ Subject: Resources consumed by unit runtime
░░ Defined-By: systemd
░░ Support: https://gentoo.org/support/
░░
░░ The unit nut-monitor.service completed and consumed the indicated resources.
More information about the Nut-upsuser
mailing list