[Nut-upsuser] Edge case in our NUT deployment, asking for guidance
Arthur Desplanches
adesplanches at buf.com
Fri Apr 15 11:44:03 BST 2022
Hi,
I'm working on deploying NUT for our main server room, and I've put
myself in a situation where there could be an edge case that I don't
really like, and so I'm asking for a bit of guidance.
Most of the deploymentis fairly standard according to the documentation
(big thanks for its exhaustiveness, by the way), the main change is my
shutdown script. It checks if we have power on both PSUs using IPMI, and
if this is the case, it doesn't shut down (in any other case it does :
ipmi doesn't work, only one PSU is receiving power, only one PSU exists
on the machine, etc). We did this because about 90% of our machines have
dual redundant PSUs, with one on the UPS, the other on mains buton a
separate circuit. So we could have a situation where the UPS loses
power, but we still have some on a secondary circuit.
We choose to accept the fact that if the secondary circuit loses power
after our NUT server sent a force shutdown sequence, we may have a bad
shutdown at this point.
What could happen in this situation, is that a machine that is a
nut-server (A) still has the FSD flag running (because it didn't shut
itself down) even after power comes back and some machines restart. In
this case, the upsmon on the freshly started machines will see the flag
and then shut themselves down again.
Our workaround currently would be to be aware of this and restart
nut-server and then nut-monitor on the machine A before starting back
any of its clients that is currently down.
Is there any idea of a better way to handle this edge case ? Or a better
way to articulate this ? Maybe a way to automatically clear the FSD flag ?
Thanks for the help
Arthur
--