[Nut-upsuser] How to change shutdown notification threshold on Fortron UPS Champs (blazer_usb)?
    Roger Price 
    roger at rogerprice.org
       
    Mon Aug 29 14:14:14 BST 2022
    
    
  
On Mon, 29 Aug 2022, Pavel Hofman wrote:
blazer_usb reports:
>> ups.model: WPHVT2K0
>> ups.productid: 5161
The Fortron site https://energy.fsp-europe.com/uninterruptible-power-supply/ has 
no mention of these references.  I wonder where blazer_usb found them?
>> ups.status: OL
If you unplug the UPS from the wall, and run it down, maybe with a dummy load, 
do you see OB, LB, other statuses?
>> battery.voltage.high/nominal/low: 52.00/48.0/41.60
Does the battery.voltage drop regularly as the UPS exhausts itself?
If battery.charge.low is not available, perhaps it is possible to get the same 
effect by watching the voltage drop to a critical value.  This needs upssched 
and a custom upssched-cmd script.
The alternative is to shutdown after a fixed time in status OB.  Its my 
preferred solution since I live in an area with a lot of lightning strikes, but 
few people seem to do it.
Roger
    
    