[Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade

Simon Wilson simon at simonandkate.net
Fri Dec 2 00:35:12 GMT 2022


Resending as original was too big for list acceptance.

Hi Bill,

/etc/systemd/system/nut-driver at .service.d/environ.conf sets the  
nut-driver service's environment variable, such that it sees a  
workable NUT_STATEPATH of /var/run/nut when upsdrvctl is run by the  
service, regardless of what is set in upsd.conf, and explains why the  
driver worked yesterday but upsd didn't.

Tests which may be interesting:

1. First test:- move nut-driver's environ.conf file to somewhere else  
temporarily; leave upsd.conf STATEPATH uncommented saying /run/nut;  
restart nut-driver at cyberpower.service; and see if it runs. This tests  
to see if it *needs* the drop-in service file *or* will work with only  
STATEPATH explicitly set in upsd.conf to /run/nut.  If this prevents  
the driver from working, put the environ.conf file back (but edit it,  
it should say /run/nut, not /var/run/nut)

2. Second test:- copy the edited  
/etc/systemd/system/nut-driver at .service.d/environ.conf to  
/etc/systemd/system/nut-server.service.d/environ.conf. So you should  
at that point have both locations with a file saying
   [Service]
   Environment=NUT_STATEPATH=/run/nut
Then comment out STATEPATH line (back to default) in upsd.conf and  
restart nut-server - does it still start, and does it still pop a  
"Could not find PID file '/var/run/upsd.pid'" message? That tests  
whether the drop-in file is a better, more consistent fix for now  
(until the packages are resolved). Calling the nut-server process with  
that variable set for upsd *even before it reads upsd.conf* may remove  
the first error 'Could not find PID file '/var/run/upsd.pid''

And definitely document any changes you make to your setup as  
subsequent package releases will likely change all of this :)

Couple more comments inline below.

Simon


----- Message from Bill Gee <bgee at campercaver.net> ---------
   Date: Thu, 1 Dec 2022 16:49:14 -0600
   From: Bill Gee <bgee at campercaver.net>
Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade
     To: nut-upsuser at alioth-lists.debian.net

> Checking now - There is a file called  
> /etc/systemd/system/nut-driver at .service.d/environ.conf.  Its  
> contents are
>
> ==========================
> [root at mythtv nut-driver at .service.d]# ll
> total 8
> -rw-r--r-- 1 root root 49 Nov 29 18:14 environ.conf
> -rw-r--r-- 1 root root 81 Nov 30 18:58  
> nut-driver-enumerator-generated-checksum.conf
>
> [root at mythtv nut-driver at .service.d]# cat environ.conf
> [Service]
> Environment=NUT_STATEPATH=/var/run/nut
>
> ==========================
>
> Which explains, I think, much of the problem.  I do not remember  
> putting that file in place.  However, it is dated 29 Nov, just a  
> couple of days ago, so it was probably me who did it.

It's not a default file, so yes it was you - this was a suggestion I  
made earlier in the week (although I suggested it should say /run/nut  
not /var/run/nut), and with it there explains why the driver works  
before you uncommented STATEPATH in upsd.conf.

>
> Should I delete the file?  Or change it to use /run/nut?

See comments on tests at the top of this email.

>
> And that raises another interesting question:  Since /var/run and  
> /run are effectively the same thing, why does /run work and /var/run  
> not work?

What makes you think one works and the other does not? They *are*  
functionally the same thing (excepting a harmless warning message  
about using /var).

>
> ===============
> Bill Gee
>
> On 12/1/22 16:38, Simon Wilson via Nut-upsuser wrote:
>> Working nut-driver, working nut-server. That's a lot further than  
>> you were on Tuesday.
>>
>> It's a little odd that nut-driver worked without STATEPATH being  
>> uncommented in upsd.conf but nut-server needed the change.
>> @Jim, without digging into source, any reason why that would be the case?
>> @Bill, you didn't end up doing an 'environ.conf'-style drop-in file  
>> at '/etc/systemd/system/nut-driver at .service.d/' did you (as that  
>> would explain the difference between the two services)?
>>
>> You will need to enable nut.target to have things start on boot,  
>> and reboot to make sure everything starts OK.
>>
>> Simon
>>
>> ----- Message from Bill Gee <bgee at campercaver.net> ---------
>>    Date: Thu, 1 Dec 2022 10:43:04 -0600
>>    From: Bill Gee <bgee at campercaver.net>
>> Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade
>>      To: nut-upsuser at alioth-lists.debian.net
>>
>>> My email client (Thunderbird) does not truncate, but it does  
>>> wrap.  The truncations come from the way systemctl runs its output  
>>> through a pager. When I copy-paste from the bash session, it  
>>> truncates at the right edge of the window.   I need to use the  
>>> --full and --no-pager options to get the full text, which will be  
>>> wrapped as needed.
>>>
>>> Here is the output from upsd -DD:
>>>
>>> ===================================
>>> [root at mythtv ~]# upsd -DD
>>> Network UPS Tools upsd 2.8.0
>>>   0.000000     fopen /var/run/upsd.pid: No such file or directory
>>>   0.000030     Could not find PID file '/var/run/upsd.pid' to see  
>>> if previous upsd instance is already running!
>>>
>>>   0.000250     [D1] debug level is '2'
>>>   0.000335     listening on ::1 port 3493
>>>   0.000375     listening on 127.0.0.1 port 3493
>>>   0.001417     /var/run is world readable
>>>   0.001557     Can't connect to UPS [cyberpower]  
>>> (usbhid-ups-cyberpower): No such file or directory
>>>   0.002315     Running as foreground process, not saving a PID file
>>>   0.002337     [D1] mainloop: UPS [cyberpower] is not currently connected
>>>   0.002377     [D1] mainloop: UPS [cyberpower] is now connected as FD -1
>>>   0.002399     [D2] mainloop: polling 2 filedescriptors
>>>   2.003794     [D2] mainloop: no data available
>>>   2.003842     [D1] mainloop: UPS [cyberpower] is not currently connected
>>>   2.003897     [D1] mainloop: UPS [cyberpower] is now connected as FD -1
>>>   2.003917     [D2] mainloop: polling 2 filedescriptors
>>>   4.005963     [D2] mainloop: no data available
>>>   4.006009     [D1] mainloop: UPS [cyberpower] is not currently connected
>>>   4.006054     [D1] mainloop: UPS [cyberpower] is now connected as FD -1
>>>   4.006073     [D2] mainloop: polling 2 filedescriptors
>>>   6.008122     [D2] mainloop: no data available
>>> ==============================
>>>
>>> Just for grins, I edited /etc/ups/upsd.conf to uncomment the  
>>> STATEPATH line.  I set it to /run/nut.  When I ran upsd -DD again,  
>>> it was still looking at /var/run.  However!  It successfully  
>>> connected to the cyberpower device.  Upsc returns good information.
>>>
>>> =================================
>>> [root at mythtv ups]# upsd -DD
>>> Network UPS Tools upsd 2.8.0
>>>   0.000000     fopen /var/run/upsd.pid: No such file or directory
>>>   0.000037     Could not find PID file '/var/run/upsd.pid' to see  
>>> if previous upsd instance is already running!
>>>
>>>   0.000271     [D1] debug level is '2'
>>>   0.000357     listening on ::1 port 3493
>>>   0.000395     listening on 127.0.0.1 port 3493
>>>   0.001550     Connected to UPS [cyberpower]: usbhid-ups-cyberpower
>>>   0.002323     Running as foreground process, not saving a PID file
>>>   0.002347     [D2] mainloop: polling 3 filedescriptors
>>>   0.002423     [D2] mainloop: polling 3 filedescriptors
>>>   0.002493     [D2] mainloop: polling 3 filedescriptors
>>>   0.002570     [D2] mainloop: polling 3 filedescriptors
>>>   0.002648     [D2] mainloop: polling 3 filedescriptors
>>>   0.002701     [D2] mainloop: polling 3 filedescriptors
>>>   2.004311     [D2] mainloop: no data available
>>>   2.004352     [D2] mainloop: polling 3 filedescriptors
>>>   4.006061     [D2] mainloop: no data available
>>>
>>> [root at mythtv ups]# systemctl --full --no-pager status nut-server
>>> ● nut-server.service - Network UPS Tools - power devices information server
>>>     Loaded: loaded (/usr/lib/systemd/system/nut-server.service;  
>>> disabled; preset: disabled)
>>>     Active: active (running) since Thu 2022-12-01 10:35:01 CST; 18s ago
>>>   Main PID: 3445 (upsd)
>>>      Tasks: 1 (limit: 9482)
>>>     Memory: 732.0K
>>>        CPU: 4ms
>>>     CGroup: /system.slice/nut-server.service
>>>             └─3445 /usr/sbin/upsd -F
>>>
>>> Dec 01 10:35:01 mythtv.billgee.local nut-server[3445]: fopen  
>>> /var/run/upsd.pid: No such file or directory
>>> Dec 01 10:35:01 mythtv.billgee.local nut-server[3445]: Could not  
>>> find PID file '/var/run/upsd.pid' to see if previous upsd instance  
>>> is already running!
>>> Dec 01 10:35:01 mythtv.billgee.local nut-server[3445]: listening  
>>> on ::1 port 3493
>>> Dec 01 10:35:01 mythtv.billgee.local nut-server[3445]: listening  
>>> on 127.0.0.1 port 3493
>>> Dec 01 10:35:01 mythtv.billgee.local upsd[3445]: listening on ::1 port 3493
>>> Dec 01 10:35:01 mythtv.billgee.local upsd[3445]: listening on  
>>> 127.0.0.1 port 3493
>>> Dec 01 10:35:01 mythtv.billgee.local nut-server[3445]: Connected  
>>> to UPS [cyberpower]: usbhid-ups-cyberpower
>>> Dec 01 10:35:01 mythtv.billgee.local upsd[3445]: Connected to UPS  
>>> [cyberpower]: usbhid-ups-cyberpower
>>> Dec 01 10:35:01 mythtv.billgee.local upsd[3445]: Running as  
>>> foreground process, not saving a PID file
>>> Dec 01 10:35:01 mythtv.billgee.local nut-server[3445]: Running as  
>>> foreground process, not saving a PID file
>>>
>>> [root at mythtv ups]# upsc cyberpower at localhost
>>> battery.charge: 100
>>> battery.charge.low: 10
>>> battery.charge.warning: 20
>>> battery.mfr.date: CPS
>>> battery.runtime: 2100
>>> battery.runtime.low: 300
>>> battery.type: PbAcid
>>> battery.voltage: 13.3
>>> battery.voltage.nominal: 12
>>> device.mfr: CPS
>>> device.model: UPS CP1000AVRLCD
>>> device.type: ups
>>> driver.name: usbhid-ups
>>> [-- snip --]
>>>
>>> ===============
>>> Bill Gee
>>>
>>> On 12/1/22 06:41, Simon Wilson via Nut-upsuser wrote:
>>>> Hi Bill, well at least you now have a fully operating,  
>>>> starts-on-reboot driver - so that is progress. One thing we need  
>>>> to know which I asked but you've not answered:
>>>> "Did you need to add the environment drop-in file? At which step  
>>>> did it work?" The answer to that may change next step.
>>>>
>>>> nut-server *should* just work if there is a driver available and running.
>>>>
>>>> OK, run:
>>>>
>>>>  systemctl disable nut-server (stop it trying to run automatically)
>>>>  upsd -DD
>>>>
>>>> And then Ctrl-C to stop it once you have got output to screen  
>>>> with startup messages.
>>>>
>>>> Then copy back here the output from upsd -DD, preferably without  
>>>> truncating lines which your mail client seems to do :(
>>>>
>>>> I'm pretty sure that nut-server is using /var/run as its  
>>>> STATEPATH. Can you also include your upsd.conf, minus commented  
>>>> lines.
>>>>
>>>> Simon.
>>>>
>>>> ----- Message from Bill Gee <bgee at campercaver.net> ---------
>>>>    Date: Thu, 1 Dec 2022 06:14:10 -0600
>>>>    From: Bill Gee <bgee at campercaver.net>
>>>> Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade
>>>>      To: nut-upsuser at alioth-lists.debian.net
>>>>
>>>>> Hi Simon -
>>>>>
>>>>> I modified /usr/lib/tmpfiles.d/nut-client to use /run instead of  
>>>>> /var/run.  I checked the startup status of the nut services.
>>>>>
>>>>> =================
>>>>> [root at mythtv ~]# systemctl list-unit-files | grep -i nut
>>>>> nut-driver-enumerator.path  enabled         disabled
>>>>> nut-driver-enumerator.service  enabled         disabled
>>>>> nut-driver at .service  indirect        disabled
>>>>> nut-monitor.service  disabled        disabled
>>>>> nut-server.service  enabled         disabled
>>>>> nut-driver.target  disabled        disabled
>>>>> nut.target  disabled        disabled
>>>>> ==========================
>>>>>
>>>>> I did a shutdown/reboot on the system.  The usbhid driver loaded  
>>>>> without errors and did not complain about /var/run.  /run/nut  
>>>>> exists and contains the expected two files.
>>>>>
>>>>> nut-server also started since it is set to "enabled", but failed  
>>>>> to connect to the driver.  It complains about "no such file or  
>>>>> directory". What file is it looking for?  I ran journalctl on it  
>>>>> but got nothing more than what systemctl status reports.
>>>>>
>>>>> ===========================
>>>>> [root at mythtv ~]# systemctl status nut-driver at cyberpower
>>>>> ● nut-driver at cyberpower.service - Network UPS Tools - device  
>>>>> driver for NUT device 'cyberpower'
>>>>>      Loaded: loaded  
>>>>> (/usr/lib/systemd/system/nut-driver at .service; enabled; preset:  
>>>>> disabled)
>>>>>     Drop-In: /etc/systemd/system/nut-driver at .service.d
>>>>>              └─environ.conf
>>>>>              /etc/systemd/system/nut-driver at cyberpower.service.d
>>>>>              └─nut-driver-enumerator-generated-checksum.conf,  
>>>>> nut-driver-enumerator-generated.conf
>>>>>      Active: active (running) since Thu 2022-12-01 05:56:04 CST; 9min ago
>>>>>     Process: 712 ExecStartPre=/usr/bin/systemd-tmpfiles --create  
>>>>> /usr/lib/tmpfiles.d/nut-client.conf (code=exited, stat>
>>>>>     Process: 719 ExecStart=/bin/sh -c  
>>>>> NUTDEV="`/usr/libexec/nut-driver-enumerator.sh  
>>>>> --get-device-for-service cyberpowe>
>>>>>    Main PID: 791 (usbhid-ups)
>>>>>       Tasks: 1 (limit: 9482)
>>>>>      Memory: 2.9M
>>>>>         CPU: 113ms
>>>>>      CGroup:  
>>>>> /system.slice/system-nut\x2ddriver.slice/nut-driver at cyberpower.service
>>>>>              └─791 /usr/sbin/usbhid-ups -a cyberpower
>>>>>
>>>>> Dec 01 05:56:04 mythtv.billgee.local nut-driver at cyberpower[787]:  
>>>>> Using subdriver: CyberPower HID 0.6
>>>>> Dec 01 05:56:04 mythtv.billgee.local nut-driver at cyberpower[787]:  
>>>>> Network UPS Tools - Generic HID driver 0.47 (2.8.0)
>>>>> Dec 01 05:56:04 mythtv.billgee.local nut-driver at cyberpower[787]:  
>>>>> USB communication driver (libusb 1.0) 0.43
>>>>> Dec 01 05:56:04 mythtv.billgee.local nut-driver at cyberpower[787]:  
>>>>> cps_adjust_battery_scale: battery readings will be sca>
>>>>> Dec 01 05:56:04 mythtv.billgee.local nut-driver at cyberpower[719]:  
>>>>> Network UPS Tools - UPS driver controller 2.8.0
>>>>> Dec 01 05:56:04 mythtv.billgee.local usbhid-ups[791]: Startup successful
>>>>>
>>>>> [root at mythtv ~]# systemctl status nut-server
>>>>> ● nut-server.service - Network UPS Tools - power devices  
>>>>> information server
>>>>>      Loaded: loaded (/usr/lib/systemd/system/nut-server.service;  
>>>>> enabled; preset: disabled)
>>>>>      Active: active (running) since Thu 2022-12-01 05:56:07 CST; 9min ago
>>>>>    Main PID: 809 (upsd)
>>>>>       Tasks: 1 (limit: 9482)
>>>>>      Memory: 1000.0K
>>>>>         CPU: 15ms
>>>>>      CGroup: /system.slice/nut-server.service
>>>>>              └─809 /usr/sbin/upsd -F
>>>>>
>>>>> Dec 01 05:56:08 mythtv.billgee.local upsd[809]: listening on ::1  
>>>>> port 3493
>>>>> Dec 01 05:56:08 mythtv.billgee.local upsd[809]: listening on  
>>>>> 127.0.0.1 port 3493
>>>>> Dec 01 05:56:08 mythtv.billgee.local nut-server[809]: /var/run  
>>>>> is world readable
>>>>> Dec 01 05:56:08 mythtv.billgee.local nut-server[809]: Can't  
>>>>> connect to UPS [cyberpower] (usbhid-ups-cyberpower): No suc>
>>>>> Dec 01 05:56:08 mythtv.billgee.local upsd[809]: /var/run is  
>>>>> world readable
>>>>> Dec 01 05:56:08 mythtv.billgee.local upsd[809]: Can't connect to  
>>>>> UPS [cyberpower] (usbhid-ups-cyberpower): No such file>
>>>>> Dec 01 05:56:10 mythtv.billgee.local nut-server[809]: Running as  
>>>>> foreground process, not saving a PID file
>>>>> Dec 01 05:56:10 mythtv.billgee.local upsd[809]: Running as  
>>>>> foreground process, not saving a PID file
>>>>> Dec 01 06:01:08 mythtv.billgee.local nut-server[809]: Can't  
>>>>> connect to UPS [cyberpower] (usbhid-ups-cyberpower): No suc>
>>>>> Dec 01 06:01:08 mythtv.billgee.local upsd[809]: Can't connect to  
>>>>> UPS [cyberpower] (usbhid-ups-cyberpower): No such file>
>>>>> ================================
>>>>>
>>>>> ===============
>>>>> Bill Gee
>>>>>
>>>>> On 11/30/22 21:14, Simon Wilson via Nut-upsuser wrote:
>>>>>> ----- Message from Bill Gee <bgee at campercaver.net> ---------
>>>>>>    Date: Wed, 30 Nov 2022 19:26:46 -0600
>>>>>>    From: Bill Gee <bgee at campercaver.net>
>>>>>> Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade
>>>>>>      To: nut-upsuser at alioth-lists.debian.net
>>>>>>
>>>>>>> Hi Simon -
>>>>>>>
>>>>>>> I ran through the steps you gave below.  To quote  
>>>>>>> Gilbert&Sullivan ... "Modified Rapture!"  I suppose I should  
>>>>>>> try a reboot to make sure everything starts properly.
>>>>>>
>>>>>> Not yet with the reboot. Baby steps... :) you have a driver  
>>>>>> running from the service file! Celebrations are in order.
>>>>>>
>>>>>> Did you need to add the environment drop-in file? At which step  
>>>>>> did it work?
>>>>>>
>>>>>>> But first, there is a problem with upsc. Also nut-server  
>>>>>>> complains that it cannot connect to the device.
>>>>>>
>>>>>> Ok, that's next... your comments are wrong way around :)  
>>>>>> nut-server not starting is why upsc doesn't give you anything.
>>>>>>
>>>>>>> /run/nut exists and contains two files.
>>>>>>>
>>>>>>> Here are some outputs:
>>>>>>>
>>>>>>> ======================================
>>>>>>> [root at mythtv ~]# journalctl -u nut-driver at cyberpower.service -f
>>>>>>> Nov 30 19:00:20 mythtv.billgee.local systemd[1]: Starting  
>>>>>>> nut-driver at cyberpower.service - Network UPS Tools - device  
>>>>>>> driver for NUT device 'cyberpower'...
>>>>>>> Nov 30 19:00:20 mythtv.billgee.local systemd-tmpfiles[28689]:  
>>>>>>> /usr/lib/tmpfiles.d/nut-client.conf:2: Line references path  
>>>>>>> below legacy directory /var/run/, updating /var/run/nut →  
>>>>>>> /run/nut; please update the tmpfiles.d/ drop-in file  
>>>>>>> accordingly.
>>>>>>
>>>>>> That line is the "noise" error I mentioned. Edit  
>>>>>> /usr/lib/tmpfiles.d/nut-client.conf to read /run/nut, not  
>>>>>> /var/run/nut
>>>>>>
>>>>>>> Nov 30 19:00:20 mythtv.billgee.local systemd-tmpfiles[28689]:  
>>>>>>> /usr/lib/tmpfiles.d/nut-client.conf:3: Line references path  
>>>>>>> below legacy directory /var/run/, updating /var/run/nut →  
>>>>>>> /run/nut; please update the tmpfiles.d/ drop-in file  
>>>>>>> accordingly.
>>>>>>
>>>>>> Ditto, although you probably don't need line 3 in the file anyway.
>>>>>>
>>>>>>> Nov 30 19:00:21 mythtv.billgee.local  
>>>>>>> nut-driver at cyberpower[28719]: Using subdriver: CyberPower HID  
>>>>>>> 0.6
>>>>>>> Nov 30 19:00:21 mythtv.billgee.local  
>>>>>>> nut-driver at cyberpower[28719]: Network UPS Tools - Generic HID  
>>>>>>> driver 0.47 (2.8.0)
>>>>>>> Nov 30 19:00:21 mythtv.billgee.local  
>>>>>>> nut-driver at cyberpower[28719]: USB communication driver (libusb  
>>>>>>> 1.0) 0.43
>>>>>>> Nov 30 19:00:21 mythtv.billgee.local  
>>>>>>> nut-driver at cyberpower[28719]: cps_adjust_battery_scale:  
>>>>>>> battery readings will be scaled by 2/3
>>>>>>> Nov 30 19:00:21 mythtv.billgee.local usbhid-ups[28769]:  
>>>>>>> Startup successful
>>>>>>> Nov 30 19:00:21 mythtv.billgee.local  
>>>>>>> nut-driver at cyberpower[28691]: Network UPS Tools - UPS driver  
>>>>>>> controller 2.8.0
>>>>>>> Nov 30 19:00:21 mythtv.billgee.local systemd[1]: Started  
>>>>>>> nut-driver at cyberpower.service - Network UPS Tools - device  
>>>>>>> driver for NUT device 'cyberpower'.
>>>>>>>
>>>>>>> [root at mythtv ups]# ll /run/nut
>>>>>>> total 4
>>>>>>> srw-rw---- 1 nut nut 0 Nov 30 19:00 usbhid-ups-cyberpower
>>>>>>> -rw-r--r-- 1 nut nut 6 Nov 30 19:00 usbhid-ups-cyberpower.pid
>>>>>>>
>>>>>>> [root at mythtv ups]# systemctl --no-pager --full status nut-server
>>>>>>> ● nut-server.service - Network UPS Tools - power devices  
>>>>>>> information server
>>>>>>>      Loaded: loaded  
>>>>>>> (/usr/lib/systemd/system/nut-server.service; enabled; preset:  
>>>>>>> disabled)
>>>>>>>      Active: active (running) since Wed 2022-11-30 19:06:53  
>>>>>>> CST; 13min ago
>>>>>>>    Main PID: 28918 (upsd)
>>>>>>>       Tasks: 1 (limit: 9482)
>>>>>>>      Memory: 736.0K
>>>>>>>         CPU: 20ms
>>>>>>>      CGroup: /system.slice/nut-server.service
>>>>>>>              └─28918 /usr/sbin/upsd -F
>>>>>>>
>>>>>>> Nov 30 19:06:53 mythtv.billgee.local nut-server[28918]:  
>>>>>>> /var/run is world readable
>>>>>>> Nov 30 19:06:53 mythtv.billgee.local upsd[28918]: /var/run is  
>>>>>>> world readable
>>>>>>> Nov 30 19:06:53 mythtv.billgee.local upsd[28918]: Can't  
>>>>>>> connect to UPS [cyberpower] (usbhid-ups-cyberpower):  
>>>>>>> Connection refused
>>>>>>> Nov 30 19:06:53 mythtv.billgee.local nut-server[28918]: Can't  
>>>>>>> connect to UPS [cyberpower] (usbhid-ups-cyberpower):  
>>>>>>> Connection refused
>>>>>>> Nov 30 19:06:53 mythtv.billgee.local nut-server[28918]:  
>>>>>>> Running as foreground process, not saving a PID file
>>>>>>> Nov 30 19:06:53 mythtv.billgee.local upsd[28918]: Running as  
>>>>>>> foreground process, not saving a PID file
>>>>>>> Nov 30 19:11:53 mythtv.billgee.local nut-server[28918]: Can't  
>>>>>>> connect to UPS [cyberpower] (usbhid-ups-cyberpower):  
>>>>>>> Connection refused
>>>>>>> Nov 30 19:11:53 mythtv.billgee.local upsd[28918]: Can't  
>>>>>>> connect to UPS [cyberpower] (usbhid-ups-cyberpower):  
>>>>>>> Connection refused
>>>>>>> Nov 30 19:16:53 mythtv.billgee.local nut-server[28918]: Can't  
>>>>>>> connect to UPS [cyberpower] (usbhid-ups-cyberpower):  
>>>>>>> Connection refused
>>>>>>> Nov 30 19:16:53 mythtv.billgee.local upsd[28918]: Can't  
>>>>>>> connect to UPS [cyberpower] (usbhid-ups-cyberpower):  
>>>>>>> Connection refused
>>>>>>>
>>>>>>> [root at mythtv ups]# ps ax | grep ups
>>>>>>>     768 ?        Ss     0:00 /usr/sbin/cupsd -l
>>>>>>>     773 ?        Ss     0:00 sshd: /usr/sbin/sshd -D  
>>>>>>> [listener] 0 of 10-100 startups
>>>>>>>   28769 ?        Ss     0:00 /usr/sbin/usbhid-ups -a cyberpower
>>>>>>>   28918 ?        Ss     0:00 /usr/sbin/upsd -F
>>>>>>>   28929 pts/1    S+     0:00 grep --color=auto ups
>>>>>>>
>>>>>>> [root at mythtv ups]# upsc cyberpower at localhost
>>>>>>> Error: Driver not connected
>>>>>>
>>>>>> upsc won't work without nut-server running, so this is expected  
>>>>>> based on the above failure to start nut-server.
>>>>>>
>>>>>>>  
>>>>>>
>>>>>> So... next.
>>>>>>
>>>>>> Fix nut-client.conf contents, and make sure that you can start  
>>>>>> / restart the driver as needed with no errors. Set  
>>>>>> nut-driver at cyberpower.service to enabled for autostart, so with  
>>>>>> ONLY the enumerator services and nut-driver at cyberpower.service  
>>>>>> enabled, you should see something like the following for  
>>>>>> 'systemctl list-unit-files | grep -i nut':
>>>>>>
>>>>>> [root at emp80 ups]# systemctl list-unit-files | grep -i nut
>>>>>> nut-driver-enumerator.path                                       
>>>>>>        enabled
>>>>>> nut-driver-enumerator.service                                   
>>>>>>         enabled
>>>>>> nut-driver at .service                                             
>>>>>>         indirect
>>>>>> nut-monitor.service                                             
>>>>>>         disabled
>>>>>> nut-server.service                                               
>>>>>>        disabled
>>>>>> nut-driver.target                                               
>>>>>>         disabled
>>>>>> nut.target                                                       
>>>>>>        disabled
>>>>>>
>>>>>> Stop any running nut processes, and reboot. On reboot the only  
>>>>>> thing that should autostart is nut-driver at cyberpower.service  
>>>>>> (from the 'indirect' call via nut-driver at .service). upsc will  
>>>>>> still not work.
>>>>>>
>>>>>> Monitor the driver for a while 'journalctl -u  
>>>>>> nut-driver at cyberpower.service -f' and make sure it is stable  
>>>>>> and stays connected - google searches show some flakiness with  
>>>>>> some cyberpower UPSs.
>>>>>>
>>>>>> Once you are confident that the driver is reliable, starting OK  
>>>>>> and staying up then move on to nut-server.
>>>>>>
>>>>>> I'll check in this evening and we can do some more digging on that.
>>>>>>
>>>>>> Simon
>>>>>>
>>>>>>> ===============
>>>>>>> Bill Gee
>>>>>>>
>>>>>>> On 11/30/22 07:21, Simon Wilson via Nut-upsuser wrote:
>>>>>>>> Comments inline.
>>>>>>>>
>>>>>>>> ----- Message from Bill Gee <bgee at campercaver.net> ---------
>>>>>>>>    Date: Wed, 30 Nov 2022 06:04:14 -0600
>>>>>>>>    From: Bill Gee <bgee at campercaver.net>
>>>>>>>> Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 ->  
>>>>>>>> 2.8 upgrade
>>>>>>>>      To: nut-upsuser at alioth-lists.debian.net
>>>>>>>>
>>>>>>>>> Hi Simon --
>>>>>>>>>
>>>>>>>>> Yes, I am pretty sure this is the RedHat packaging problem.   
>>>>>>>>> I sure hope they get it squared away.  I have only one  
>>>>>>>>> system using nut and that is because all my other systems  
>>>>>>>>> have APC battery backup and run apcupsd. Apcupsd may be old,  
>>>>>>>>> grey and unmaintained, but it Just Works.
>>>>>>>>>
>>>>>>>>> You mention that the STATEPATH line in upsd.conf will  
>>>>>>>>> override other settings.  It does not appear to be the case  
>>>>>>>>> for me.  The only way I could get the driver to run was by  
>>>>>>>>> setting NUT_STATEPATH on the command line.  Perhaps that is  
>>>>>>>>> an issue with the driver and not nut-server?
>>>>>>>>>
>>>>>>>>> In answer to your questions:
>>>>>>>>>
>>>>>>>>> 1) /usr/lib/systemd/system/nut-driver at .service exists.  I  
>>>>>>>>> have made no changes to it so far.  Here are the contents,  
>>>>>>>>> unfortunately line-wrapped by Thunderbird.
>>>>>>>>>
>>>>>>>>> ================================
>>>>>>>>> [root at mythtv system]# grep -v '^#' nut-driver at .service
>>>>>>>>> [Unit]
>>>>>>>>> Description=Network UPS Tools - device driver for %I
>>>>>>>>> After=local-fs.target
>>>>>>>>>
>>>>>>>>> PartOf=nut-driver.target
>>>>>>>>>
>>>>>>>>> [Service]
>>>>>>>>> EnvironmentFile=-/etc/ups/nut.conf
>>>>>>>>> SyslogIdentifier=%N
>>>>>>>>> ExecStartPre=-/usr/bin/systemd-tmpfiles --create  
>>>>>>>>> /usr/lib/tmpfiles.d/nut-client.conf
>>>>>>>>> ExecStart=/bin/sh -c  
>>>>>>>>> 'NUTDEV="`/usr/libexec/nut-driver-enumerator.sh  
>>>>>>>>> --get-device-for-service %i`" && [ -n "$NUTDEV" ] || { echo  
>>>>>>>>> "FATAL: Could not find a NUT device section for service unit  
>>>>>>>>> %i" >&2 ; exit 1 ; } ; /usr/sbin/upsdrvctl start "$NUTDEV"'
>>>>>>>>> ExecStop=/bin/sh -c  
>>>>>>>>> 'NUTDEV="`/usr/libexec/nut-driver-enumerator.sh  
>>>>>>>>> --get-device-for-service %i`" && [ -n "$NUTDEV" ] || { echo  
>>>>>>>>> "FATAL: Could not find a NUT device section for service unit  
>>>>>>>>> %i" >&2 ; exit 1 ; } ; /usr/sbin/upsdrvctl stop "$NUTDEV"'
>>>>>>>>> StartLimitInterval=0
>>>>>>>>> Restart=always
>>>>>>>>> RestartSec=15s
>>>>>>>>> Type=forking
>>>>>>>>>
>>>>>>>>> [Install]
>>>>>>>>> WantedBy=nut-driver.target
>>>>>>>>> ===================================
>>>>>>>>
>>>>>>>> OK, so that's the same as mine. It's ExecStartPre task is to  
>>>>>>>> create the pid folder from your answer to the third (unasked)  
>>>>>>>> question :) which is that outlined in  
>>>>>>>> /usr/lib/tmpfiles.d/nut-client.conf
>>>>>>>>
>>>>>>>> You have /var/run/nut 0770 root nut - so systemd should  
>>>>>>>> ensure that exists.
>>>>>>>>
>>>>>>>> By the way, having it with "/var/run/nut" will trigger a  
>>>>>>>> 'noise' error about the "/var" path - change it to just be  
>>>>>>>> /run/nut in nut-client.conf.
>>>>>>>>
>>>>>>>> As a test, what happens if you:
>>>>>>>>
>>>>>>>> - make sure nut.conf has MODE=standalone
>>>>>>>> - make sure ALL nut services are stopped, i.e. 'ps -ax | grep  
>>>>>>>> ups' should give you only the grep process as an answer
>>>>>>>> - delete /run/nut folder (it will get re-created automatically)
>>>>>>>> - take /etc/ups/upsd.conf back to have commented out  
>>>>>>>> STATEPATH as distributed in the package
>>>>>>>> - run "systemctl enable nut-driver-enumerator.path  
>>>>>>>> nut-driver-enumerator.service --now" - this will enable and  
>>>>>>>> start the services that monitor ups.conf for changes and then  
>>>>>>>> write the actual driver service file; the second one also  
>>>>>>>> runs early in boot and ensures that the service file exists  
>>>>>>>> and is correct.
>>>>>>>> - run 'nut-scanner -U' and copy its output into ups.conf  
>>>>>>>> instead of your current definition with name heading  
>>>>>>>> [cyberpower], save and exit: this will trigger the above  
>>>>>>>> enumerators to run and re-do the  
>>>>>>>> nut-driver at cyberpower.service file
>>>>>>>>
>>>>>>>> Based on an out of the box install, you have at this point  
>>>>>>>> done enough that the driver should run (*should*!!!!)
>>>>>>>>
>>>>>>>> - run "journalctl -u nut-driver at cyberpower.service -f" in one  
>>>>>>>> terminal while you run "systemctl start  
>>>>>>>> nut-driver at cyberpower.service" in another - what does  
>>>>>>>> journalctl output?
>>>>>>>>
>>>>>>>> Assuming it does not start (based on what you have said  
>>>>>>>> below), show the messages.
>>>>>>>>
>>>>>>>> If it still does not start as configured above, but you \can/  
>>>>>>>> run /usr/sbin/usbhid-ups with your environment variables  
>>>>>>>> specified like you had done before, and it *does* run, then  
>>>>>>>> do the following steps to create a systemd drop-in file for  
>>>>>>>> the variable, but make the steps use /run/nut instead of  
>>>>>>>> /var/run/nut:   
>>>>>>>> https://bugzilla.redhat.com/show_bug.cgi?id=2127269#c8   
>>>>>>>> (comment 8, formatted for ease of reading). You want to get  
>>>>>>>> back to the RH/Fedora default of using /run/nut, not  
>>>>>>>> /var/state/ups
>>>>>>>>
>>>>>>>>   1. uncomment the "STATEPATH /var/run/nut" as already mentioned
>>>>>>>>   2. create: /etc/systemd/system/nut-driver at .service.d/environ.conf
>>>>>>>>    with these two lines:
>>>>>>>>
>>>>>>>>     [Service]
>>>>>>>>     Environment=NUT_STATEPATH=/var/run/nut
>>>>>>>>
>>>>>>>>   3. and finally do: systemctl daemon-reload
>>>>>>>>
>>>>>>>> ...then try and run systemctl start  
>>>>>>>> nut-driver at cyberpower.service again, while monitoring  
>>>>>>>> journalctl.
>>>>>>>>
>>>>>>>> If that does not work - then I'm out of ideas at this point lol... :-D
>>>>>>>>
>>>>>>>> 'set' has nothing BTW on my working system related to nut.
>>>>>>>>
>>>>>>>>> 2) In /etc/ups/upsd.conf, the original STATEPATH line is
>>>>>>>>>
>>>>>>>>> STATEPATH /var/run/nut
>>>>>>>>>
>>>>>>>>> Right now the original line is commented and I added another  
>>>>>>>>> line to point at /var/state/ups.
>>>>>>>>>
>>>>>>>>> 3) You only asked two questions, but I sense a third might  
>>>>>>>>> be important.  Originally the system had  
>>>>>>>>> /usr/lib/tmpfiles.d/nut-common.conf.  I have modified that  
>>>>>>>>> file and no longer have the original.  I copied that file to  
>>>>>>>>> nut-client.conf, and both have the same contents:
>>>>>>>>>
>>>>>>>>> =======================
>>>>>>>>> # State file (e.g. upsd to driver) and pidfile location for NUT:
>>>>>>>>> D /var/run/nut 0770 root nut - -
>>>>>>>>> X /var/run/nut
>>>>>>>>> ========================
>>>>>>>>>
>>>>>>>>> 4) And one more unasked question!  :-)  When I look at the  
>>>>>>>>> environment variables on the system, I see this:
>>>>>>>>>
>>>>>>>>> ========================
>>>>>>>>> [root at mythtv tmpfiles.d]# set | grep -i nut
>>>>>>>>> _=/etc/ups/nut.conf
>>>>>>>>> ========================
>>>>>>>>>

<snip to reduce message size>


-- 
Simon Wilson
M: 0400 12 11 16





More information about the Nut-upsuser mailing list